The NEC 100 definition for a wet location includes "unprotected
locations exposed to the weather." Obviously the roof is a wet location.
NEC 334.1(A) says NM cable is permitted in normally dry locations and
334.1(B) says it shall not be used in damp or wet locations. That said,
inspectors here have allowed a short length (up to 18" stub) of NM cable
through conduit to a j-box or outlet on the roof provided that the box
and cover are appropriate for the location. This is a topic that you
should probably address with the inspector when your project permit is
pulled. Don't expect everyone to accept this practice. You might need a
j-box in the attic to change wire type to NMC cable or THWN wire.
Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
On 11/1/2012 5:07 AM, Chris Mason wrote:
I remember from a project we were doing that required Romex that it is
listed for damp locations such as outdoor areas likely to see some
rain, wet locations are literally underwater rated and designate
conduits running underground likely to flood.
On Wed, Oct 31, 2012 at 10:50 AM, Glenn Burt <[email protected]
<mailto:[email protected]>> wrote:
Seems if the Romex is not listed as being suitable for use in a
wet location, having not been tested by UL for that situation, it
would not be suitable for use in that environment, regardless of
how its internal conductors are rated.
Glenn Burt
*From:*Ray Walters [mailto:[email protected]
<mailto:[email protected]>]
*Sent:* Friday, October 26, 2012 10:28 PM
*To:* [email protected] <mailto:[email protected]>; RE-wrenches
*Subject:* Re: [RE-wrenches] Enphase and Romex
So if the Romex is loaded with THHN/THWN (damp/wet rated), and no
where does the outer covering of the Romex itself get exposed to
the wet location, that should be sufficient?
Ray Walters
On 10/26/2012 7:45 PM, Glenn Burt wrote:
300.9 Raceways in Wet Locations Above Grade.
Where raceways are installed in wet locations abovegrade, the
interior of these raceways shall be considered to be a wet
location. Insulated conductors and cables installed in
raceways in wet locations abovegrade shall comply with 310.8(C).
"Section 300.9, new for the 2008 Code and similar to 300.5(B),
draws attention to the inside of all raceways and enclosures
installed in an abovegrade wet location. The inside of these
raceways and enclosures now definitively requires conductors
and cables suitable for use in wet locations in accordance
with to 310.8." -- Explanatory note
310.8 Locations.
(C) Wet Locations. Insulated conductors and cables used in wet
locations shall comply with one of the following:
(1) Be moisture-impervious metal-sheathed
(2) Be types MTW, RHW, RHW-2, TW, THW, THW-2, THHW,
THWN, THWN-2, XHHW, XHHW-2, ZW
(3) Be of a type listed for use in wet locations
*From:*[email protected]
<mailto:[email protected]>
[mailto:[email protected]] *On Behalf
Of *benn kilburn
*Sent:* Friday, October 26, 2012 2:03 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Enphase and Romex
Glenn/Jason,
So you wouldn't use romex to feed an exterior outlet on an
outside wall, or to any outside lights???
Canadian Electrical Code's (CE Code) definitions...
_wet location_ -a location in which liquids may drip, splash,
or flow on or against electrical equipment.
_Damp location_--an exterior or interior location that is
normally or periodically subject to condensation of moisture
in, on, or, adjacent to electrical equipment an includes
partially protected locations under canopies, parquees, roofed
open porches, and similar locations.
_Dry location _--a location not normally subject to dampness,
but that may include a location subject to temporary dampness
as in the case of a building under construction, provided that
ventilation is adequate to prevent an accumulation of moisture.
If inside your attic is considered a "wet location", then you
have other issues. Are you sure the NEC's definition of 'wet
location' is relating to the location of the romex?
I just spoke to one of my inspectors and he sees no issue with
entering the bottom of a soladeck with romex.
On the grounding/bonding, I have been using the bare wire in
the romex for the enphase system ground (within the enphase
cable) and running a #6 from the mod frames and rails into the
soladeck and along side the romex back to the panelboard.
I need to get myself a copy of your NEC so I can be on the
same page as you guys. I hear it is written in a way that is
much easier to interpret than the CE Code, which is written in
a very legal jargon.
Cheers,
benn
DayStar Renewable Energy Inc.
www.daystarsolar.ca <http://www.daystarsolar.ca> * Ph:
780-906-7807 <tel:780-906-7807>
Construction Electrician Solar Photovoltaic Systems Certified
Certificate # 0007S
HAVE A SUNNY DAY
On 25/10/12 9:37 AM, "Glenn Burt" <[email protected]
<mailto:[email protected]>> wrote:
Soladeck on the rooftop places it in an environment that is
considered 'wet'.
I don't think Romex is listed for use in a wet environment.
This would force you to use the proposed jbox in the attic for
the transition location.
I also understood that you could combine the EGC and GEC into
a single conductor as long as it is continuous or irreversibly
spliced, as part of the '08 code.
-Glenn Burt
*From:*[email protected]
<mailto:[email protected]>
[mailto:[email protected]] *On Behalf
Of *Jason Szumlanski
*Sent:* Thursday, October 25, 2012 9:13 AM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Enphase and Romex
I'm sure this has been covered, but I could not find it in the
archives.
We are considering using Romex in the attic for the first
time. My plan was to use the new Enphase coupler to connect
the trunk cable to Type TC-ER, enter a Soladeck passthrough
box on the roof into a junction box in the attic where I would
make the transition to 10/3 Romex. I'm hung up on the GEC
going back to the service panel. Any suggestions?
By the way, we are on NEC 2008, and in most cases there is
also a requirement for an additional grounding electrode per
NEC 690.47(D) (that shouldn't really relate to my issue).
*Jason Szumlanski*//
/Fafco Solar/
_______________________________________________ List sponsored
by Home Power magazine List Address:
[email protected]
<mailto:[email protected]> Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette: www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm> Check out
participant bios: www.members.re-wrenches.org
<http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Home Power magazine
List Address:[email protected]
<mailto:[email protected]>
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
<mailto:[email protected]>
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
--
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com <http://www.cometenergysystems.com>
Cell: 264.235.5670
Skype: netconcepts
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org