There is no need for an exception. Even in the 2008 NEC, 690.31(E) is clearly about the dc wiring. The proposed informational note adds nothing except to explain that ac isn't dc.

Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
On 11/3/2012 11:09 AM, Dan Fink wrote:
There is an proposal in the pipeline for NEC 2014 that makes an exception for AC PV modules after the wiring enters the building. See: http://www.solarabcs.org/codes-standards/NFPA/pdfs/2014NEC%20690.31(E).pdf <http://www.solarabcs.org/codes-standards/NFPA/pdfs/2014NEC%20690.31%28E%29.pdf>
--
Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342 (voicemail)

On Sat, Nov 3, 2012 at 10:19 AM, David Brearley <david.brear...@solarprofessional.com <mailto:david.brear...@solarprofessional.com>> wrote:

    FWIW: In the 2011 Code, Section 690.31(D) is changed to include
    the following:

    "Where dc photovoltaic source or output circuits...are run inside
    a building or restructure, they shall be contained in metal
    raceways,/Type MC metal-clad cable that complies with
    250.118(10/), or metal enclosures..."


    On Nov 3, 2012, at 10:41 AM, Nick Vida wrote:

    Hello wrenches,

    wondering if any of you are running into inspectors wanting EMT
    in the attics, or allowing flex only if there is a fusible
    disconnect on the roof. We have heard this a few time lately and
    havent yet seen a code reference, (except 690.31e saying metal
    raceways are fine- not specifying EMT only). I am wondering if
    this is a new wave of inspectors wanting the future now as
    informed by an expert seminar, or if there is something I am not
    aware of. Any comments are very appreciated.

    Thank you,

    Nick Vida
    wrench






_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to