Nick, what the AHJ is telling you may actually be in reference to 250.97; for most PV output circuits (yes these are necessarily dc) this bonding requirement applies since array VOC > 250 VDC. As Kent just pointed out, these dc conductors clearly don't meet the NEC definition of a service.

"250.97 Bonding for Over 250 Volts. For circuits of over 250 volts to ground, the electrical continuity of metal raceways and cables with metal sheaths that contain any conductor other than service conductors shall be ensured by one or more of the methods specified for services in 250.92(B), except for (B)(1)..." followed by an exception.

Seems that FMC is OK as an EGC if your conductors have <20A OCPDs, which I imagine you do, but that FMC also can't be longer than 6' (see 250.118(5)). So I think your AHJ is probably right and I just learned something. If you're running a separate EGC anyway, you may want to ask why this bonding business is so important-- but I don't have an NEC reference on this to help you argue this. Maybe the AHJ would allow you to just run MC cable as the 2011 NEC allows.

John Wiles is awesome. Someone on this list had to say it.

DKC

On 2012/11/8 23:22, Nick Vida wrote:
Hi Wrenches,

Thanks for you comments. Fun for the day is hearing they want to apply
section 230 about service conductors and say that flex is not
a metallic raceway because it is no good for bonding. They are defining
the pv source circuits as a service.
I am getting a distinct Wiles vibe here.

I find it so annoying when they try to put out these distinctions with
no code, no city ordinance and not even an internal memo, especially
when they remain obstinate without going to the trouble to actually
legitimize the interpretation.

Dan- are the output circuits necessarily DC? I would have to look at NEC
for a minute, but it doesn't seem to add up to me right now.

Thanks,

Nick Vida


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to