JASON:

The reference temperature for the Square-D breakers is 40C/104F, as opposed to 20C/68F for the ABB breakers. The possibility of a "nuisance trip" due to derating would occur sooner for a 20A ABB breaker than for a 20A QO/QOB breaker.

I received a follow-up e-mail earlier today from Steve Capozzi of SolaDeck:

-------- Original Message --------
   Subject:     RE: SolaDeck
   Date:        Tue, 27 Nov 2012 07:20:17 -0600
   From:        Steve Capozzi <[email protected]>
   Organization:        RSTC Enterprises
   To:  <[email protected]>


   Gary,

     I sent ABB engineering an e-mail yesterday to see if they have any
   new items with higher ambient temps.

   The breakers we have were the highest at the time we started into AC
   systems.

   We have never had a issue in the field with these breakers.

     I will keep you posted.

   steve

   Steve Capozzi
   President
   RSTC Enterprises Inc
   2214 Heimstead Road
   Eau Claire, Wi 54703
   866-367-7782
   715-830-9997

 I'll keep you posted with what I find out.

Regards,


Gary Willett, PE
Icarus Engineering LLC

Icarus Solar Services LLC

On 11/27/2012 8:30 AM, Jason Szumlanski wrote:
We're pretty fortunate that a roof mounted readily accessible disconnect has not been a sticking point locally. I would argue that the AC disconnect is still the trunk cable connector, which can be not readily accessible. The AC breaker carrying the combined circuit output in the main distribution panel or the fusible disconnect switch if performing a supply side connection would qualify as the readily accessible disconnect. If you install Enphase I'm sure you are familiar with the manufacturer's excellent white paper on this issue.

I hear what you are saying about the temperature concerns, but there are many installations that have far fewer than 17 inverters per string. A typical residential installation can be split into two or three branch circuits (thank you, Andrew, for keeping me accurate on the string/circuit thing!) The temp concern is definitely something to explore further. There is also the thermal interference factor to take into account for multiple breakers that Gary did not mention. The full datasheet is here:

http://www05.abb.com/global/scot/scot209.nsf/veritydisplay/11d7d0032b466358c125712400340107/$file/2CDC002052D0203_UL489.pdf

As for the "interior rated" breaker comment, typical AC branch circuit breakers (i.e. Sq D QO) are mounted in wet location NEMA 3R boxes all the time on the exterior of a building. I'm not sure I understand this concern. The temperature derating curve is also similar for ABB and QO breakers. QO Datasheet here:

http://static.schneider-electric.us/docs/Circuit%20Protection/Miniature%20Circuit%20Breakers/QO-QOB%20Circuit%20Breakers/0730CT9801R108.pdf

I definitely want to be 100% sure the SolaDeck and breakers are appropriately rated before proceeding. Any comments welcomed...

*Jason Szumlanski*//

/Fafco Solar/



On Mon, Nov 26, 2012 at 6:37 PM, Gary Willett <[email protected] <mailto:[email protected]>> wrote:

    JASON:

    I talked to Steve Capozzi of SolaDeck and he sent me additional
    info about the circuit breakers:

        _Manufacturer_:  ABB

        _Terminal Temp Rating_:  75C / 167F

        _Reference Temperature_: 20C / 68F

        _Ambient Temp Derating_:

            30C/86F = 18.7A
            40C/104F = 17.3A
            50C/122F = 15.8A
            60C/140F = 14.1A
            70C/158F = 12.2A

    My concern is that we may be attempting to use an interior rated
    AC breaker in a roof-deck-mounted NEMA3-R enclosure.

    In an Enphase application, with the maximum of 17 inverters per AC
    Source Circuit, the continuous current will be 0.9A x 17 x 1.25 =
    19.1A. This exceeds the 30C/86F trip current of 18.7A.

    The interior temperature of the SolaDeck could very likely
    approach the 60C/140F trip current of 14.1A.

    It seems to me that "nuisance trips" could be a high probability
    event.

    Does anyone have any field experience using this Soladeck option
    for a AC Source Circuit Combiner Box (SCCB)?

    Another issue, at least in some jurisdictions, is the requirement
    for a roof-top AC Disconnect.

    The SolaDeck, when used as an AC SCCB, may not meet the NEC
    Article 100 requirements in some jurisdictions for "readily
    accessible" because a tool is required to open it.

    Regards,


    Gary Willett, PE
    Icarus Engineering LLC

    Icarus Solar Services LLC

    On 11/26/2012 2:21 PM, Jason Szumlanski wrote:
    I did get some pictures and info from Soladeck. Here are some links:

    Pics:
    
https://docs.google.com/open?id=1BpiL-1SdSNNsj4wPMQrFCLHH7JT2dek_KftSJl06QLqc0yhJ_1t5oij0aEA6
    
https://docs.google.com/open?id=1cVuhZGeQNHL1IvGvNBa7v93oZyGBvjxCv5yq4AmoyJeDAITxvgMqgECR2yTv
    
https://docs.google.com/open?id=1umslTplnFyZG1eNCZE-MMi_OqrSeirFCPRBl9mFNZJ2gQkBjM5LEXnaPKy2l
    Specs:
    
https://docs.google.com/open?id=13KLAuxUHOR9al7-36reDSJJ7IMnqV3ANPnJILPnrj2xcAi0ksRj67ifKIe7R
    
https://docs.google.com/open?id=1kvPFcDc1vruS3W_aONlXyIHm1T8-qi4vTpTwGGJ7H0eIwuZ-5e6zrM1CcND5
    
https://docs.google.com/open?id=1lM8FtYl9HiYohru32UA_Gb1tXZKZ5iw-8tnSu1Un6g4vcklLL-DK1qLPMdsB

    I was told Soligent can source the combiners for you (and me).

    *Jason Szumlanski*//

    /Fafco
    
Solar/<http://www.wisestamp.com/apps/wordpress?utm_source=extension&utm_medium=email&utm_term=wordpress&utm_campaign=apps>


    On Mon, Nov 26, 2012 at 1:50 PM, Jason Szumlanski
    <[email protected] <mailto:[email protected]>> wrote:

        I just called Soladeck and they are sending me some more info
        on availability. I'll pass it along when I get it. I didn't
        realize they made an AC roof mounted string combiner
        solution. That's a huge help for 2 or 3 string Enphase
        installations (they make both combiners).

        While on the subject, we recently started using the Enphase
        cable couple with Type TC-ER cable to extend cabling to
        junction boxes when necessary... No more wasting trunk cable
        connectors! I suppose Type TC-ER could be used all the way to
        the main distribution panel, thereby eliminating junctions on
        the roof, but I haven't looked into the cost/benefit of that
        idea.

        *Jason Szumlanski*

        /Fafco Solar/




_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to