These code references should be all that is necessary to put the inspector on the right path. His requirement that the source be capable of 100 amps clearly conflicts with the intent of 690.10(A); it makes clear that the inverter system only needs to be large enough to operate the single largest load that it is intended to operate. Thus it is permissible for combinations of loads to overload the inverter and cause a nuisance shutdown.

You might also ask if he'd be happy with a utility service provided by a 15-kVA transformer. While capable of substantial overloads, it is only rated to provide 63 amps continuously. Most 200-amp service panels don't really have 200 amps available except for short durations.

Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882

On 12/12/2012 4:43 AM, Jason Szumlanski wrote:
See 690.10, 690.1, and 690.3.


*Jason Szumlanski*//

/Fafco Solar/



On Wed, Dec 12, 2012 at 1:00 AM, William Miller <[email protected] <mailto:[email protected]>> wrote:

    Jeff:

    There is a code passage that specifically states that one does not
    need to provide full rated ampacity to a service.  I am sure you
    can find it.

    Find a way to prove, mathematically, that the system planned will
    provide adequate power.  Create or find a spreadsheet listing all
    appliances and wattages and system watt hours provided.  Dress it
    up, put your logo on it and sell it to the building department.

    William Miller




    At 07:52 PM 12/11/2012, you wrote:

        Content-Type: multipart/alternative;
                boundary="----=_NextPart_000_0006_01CDD7F2.373D3CB0"
        Content-Language: en-us


        We have a client that just had assembled on his rural property
        a pre-fab modular home with  "normal" wiring and 200 amp main
        panel and meter base.  However, landowners around his property
        will not grant access for electric utility to cross and he
        needs to move in ASAP.  He realizes that some day he should be
        able to resolve this utility access but until then he wants us
        to do an off-grid "basic" solar system with generator backup
        so he can at least power lights, well pump, and basic
        appliances.   His budget will not allow a fully off-grid solar
        system so we wanted to do reduced solar and battery system
        with larger generator to fill in on bad solar days.  He does
        have good solar exposure and lots of cleared land, but figures
        one day the solar and generator will become a backup system to
        a future grid connection so does not want to spend any more
        than absolutely necessary.

        However ,this local inspector for this rural county has no
        experience with solar and is expecting to see a 200 amp
        service connection from the utility before allowing occupancy.
         He did hint that a 100 amp service connection may be allowed
        but nothing less.  I know NEC does mention that a panel does
        not have to be supplied with the amount of service capacity it
        is rated for, but what other code issues can I point out to
        get this accepted without getting into a pis----- contest?

        Thanks,

        Jeff Yago


    _______________________________________________
    List sponsored by Home Power magazine

    List Address: [email protected]
    <mailto:[email protected]>

    Options & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>




_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to