Hi Folks:

I just finished up another ugly rewire project for a customer that had another"installer" put in a Xantrex TR inverter. We fixed numerous wiring issues, including neutral bonded to ground in 7 different places! The issue we're having now though, is that the TR inverter output voltage fluctuates when running CF lighting, and the refrigerator. You can literally see the lights cycling brighter and dimmer, and hear the compressor on the fridge running up and down in frequency. Xantrex/ Schneider Tech support said that: A) The TR doesn't do well with CF lighting, and that we should switch to all incandescent........ hmmmm.
B)  We should set the search watts to zero (which I already did)
C) We need to increase the loads on the TR, as it doesn't regulate output voltage and frequency very well at lower loads........ 2nd big hmmmmm.

I knew there was a reason I quit installing Xantrex inverters about 5 years ago, but I couldn't recall the details. Now its all coming back to my feeble, aging brain. So aside from switching out the inverter , (which I just installed on a beautiful Midnite E-Panel) does anybody have any cures for our ills? How would LED lighting behave? Should I throw a capacitor across the output? or perhaps I should just retire early and sail around the Caribbean? (I can afford a canoe/ no sail......)

As always, thanks in advance for this wonderful technical (and emotional) support group,

--
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,(installation Professional now?)
Licensed Master Electrician
Solar Design Engineer
303 505-8760

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to