> I don't enjoy the PLC interference problems, which are rare. When they have 
> occurred, Enphase provided continuous technical support, including factory 
> evaluation of line filters and enhanced system analysis.  Did you know that 
> each Enphase system has a built in spectrum analyzer? Tech support can 
> provide a printout of interfering signals to help in troubleshooting. 
> Installing a separate AC load center to accept the AC return breakers helps 
> with solving these problems.  I understand that the next release of Enphase 
> inverters will be Wi-fi, eliminating the PLC protocol entirely.  When the 
> communication works, (which it does most of the time) it is a very valuable 
> resource.

I find we have several times the service calls on enphase due to the customers 
thinking their system isn't working, when in fact it the flakey PLC network. 
And all that monitoring is only really telling me about the inverters or their 
networking, since the long term failure rate of the panels is several orders of 
magnitude better than even the best inverter on the market.

I have only seen 2 Xantrex string inverters go out in the last 5 years (no 
surprise there) out of all of the string inverters, and all of the brands. But 
I've seen failure at everyone of our Enphase installs, and usually failures 
every year (1 or 2 dead micros per year per site).

There is no argument that micros improve flexibility. And the potential for a 
micro to have a higher MTBF is believable. But first they need better design, 
more market experience, and will never reach 25 year lifespan like they say 
until they take electrolytic caps out of their designs.

thanks,

Troy Harvey
---------------------
Principal Engineer
Heliocentric
801-453-9434
[email protected]


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to