Jeff
First yes a 2 wire signal wire from the Sunny Island to the Genny,
Second if this is off grid only the Sunny Boy will be programmed
with a SMA service cable to be "Off Grid Only" and then it does
not need the RS485 com cable between it and the Sunny Island. The
RS485 cable is only needed when you want the Sunny Boy to switch
between Off Grid and Grid tie.
Ryan
On 6/22/2013 10:26 PM, Jeff Clearwater wrote:
Hi Esteemed
Wrenchies,
For a totally off-grid AC Coupled Sunny Island system to
control an off-grid Kohler two-wire start generator I
assume:
1) All I need to bring is control wire besides the genny and
Sunny Island.
2) No external relays needed - all built in to the Sunny
Island and genny.
3) If no grid-tie (only generator) then no need to program
DIGIN signal as per SMA's tech note on Gen and grid systems?
Am I missing something here?
Thanks!
Jeff
--
Jeff Clearwater
Ecovillage Network of the Americas
The Visionary Commons
Ecovillage Design Consultant
www.visionarycommons.org
skype - jclearwater
cell - 413-559-9763

~~~~~~~~~~~~~~~~~~~~~~~~~~~
--
Jeff Clearwater
Village Power Design
Renewable Energy Design & Installation
Ecovillage Design Consultant
NABCEP™ Certified
Solar PV Installer
Licensed Solar
Contractor in CA - C-46
www.villagepower.com
413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
|
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org