Southern California Edison (SCE) is now denying applications for 
interconnection and net metering IF the system can charge batteries by using 
grid power. It looks like they are worried about people using time-of-use 
metering in this way.

I think it's completely bogus, not only because of the questionable economics, 
but also because if a lot of people actually do this, it will help the grid, 
and the utility, not hurt it. I don't see how charging batteries is any 
different than running any other load during off-peak.

Brian Teitelbaum
AEE Solar

From: [email protected] 
[mailto:[email protected]] On Behalf Of SunHarvest
Sent: Tuesday, June 25, 2013 10:27 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Battery bank during peak times

Hi Jesse,

If I read this correctly your customer is wanting to go off-grid during peak 
hours. I recently went through this same thing with a customer. I received 
feedback from an old SMA tech and some Wrenchers (thread titled "Battery 
Back-up and Grid Tie"). Here's what I learned:

1. Inverters are more efficient at inverting than charging, anywhere from 
5-10%. Add to that about 10% transmission loss...you'll always have significant 
energy losses associated with trying to put back that power that you're drawing 
out during those peak hours. Energy loss = $$ loss.

2. Compare the utility peak kWh cost against the cost of cycling the battery 
bank. Just for an example, let's say for a 48V system you're using 150Ah 12V 
Trojan AGMs $2000 for 8 batteries. If the specs say those batteries, at 50% 
discharge, get 1000 cycles in their lifetime, that's $2.00 per cycle. 300Ah X 
48V X 50% = 7.2kWh. $2/7.2kWh = $0.28/kWh. Add to that 20% round-trip 
efficiency losses, you're up to $0.33/kWh. What else does daily, unnecessary 
cycling add: Extra maintenance? Shortened life so probably should factor in 
some replacement cost?...

3. Murphy's law says that the power will go out at the end of one of these 
non-essential discharge cycles. Then what?

Probably not worth it.

Eric Stikes
SunHarvest
530-798-3738
----- Original Message -----
From: Jesse Dahl<mailto:[email protected]>
To: RE-wrenches<mailto:[email protected]>
Sent: Monday, June 24, 2013 8:50 PM
Subject: [RE-wrenches] Battery bank during peak times

Hello,

I was contacted by a local co-op about installing a PV system at their office.  
At first they wanted a straight grid-tied system, and after they received the 
bid they changed their minds and now want a battery based system price. What 
they want now is a system that will allow them to draw the battery bank down 
starting at 5pm during their peak demand time. Has anyone worked on or 
installed a system of this type?


Thanks as always!


Jesse
________________________________
_______________________________________________
List sponsored by Home Power magazine

List Address: 
[email protected]<mailto:[email protected]>

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to