In ungrounded systems the PV wire requirement is to be used the whole DC circuit, so that is all the way to the inverter. 690.35 (D) is pretty clear . Because it is ungrounded the protection is the PV wire's fire rating and you don't get that with thhn/thwn.
And of course Red for positive and black for negative. 
Most building departments have not pick up on this yet. But they will.  

Aram



-------- Original Message --------
Subject: Re: [RE-wrenches] double insulated wire
From: Will White <[email protected]>
Date: Fri, June 28, 2013 10:23 am
To: RE-wrenches <[email protected]>

We use PV Wire which is double insulated on the roof in free air and regular THHN/TNWN for the run from the junction box back to the inverter (using no white or gray wires of course).
 
Thanks,
Will
 
__________________________________________________________________________________________
Will White
Regional Field Operations Manager – New England
 
Real Goods Solar
64 Main St.
Montpelier, VT 05602
Tel: (802) 223-7804
Cell: (802) 234-3167
 
 
 
From: [email protected] [mailto:[email protected]] On Behalf Of Marco Mangelsdorf
Sent: Friday, June 28, 2013 1:10 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] double insulated wire
 
I’m kinda confused.  With more transformerless inverters on the market (e.g., SMA and Power-One), it’s not clear to me if double insulated wiring needs to be used all the way from each series string to their respective inverter.
 
We’ve been installing the P1 3-6 kW TL inverters and there’s no apparent mention of needing to use such conductors, yet I remember needing to do so when I installed a number of the 8, 9 and 10 kW SMA TL inverters.
 
Thanks,
marco

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to