690.35(D) does *not* require PV WIRE be used for the whole dc circuit. You can use either: (quoting directly from 2008)
1) Nonmetallic jacketed multiconductor cables
2) Conductors installed in raceways, or
3) Conductors listed and identified as PV WIRE installed as exposed, single conductors

Similarly, I don't believe that the NEC requires red and black color coding, either, though it makes the most sense given convention.

Note Brian Teitelbaum's 6/3 email about PV WIRE noting that "double-insulated" is a bit of a misnomer. Some PV WIRE is single-insulated.

DKC


On 2013/6/28 13:47, [email protected] wrote:
In ungrounded systems the PV wire requirement is to be used the whole DC circuit, so that is all the way to the inverter. 690.35 (D) is pretty clear . Because it is ungrounded the protection is the PV wire's fire rating and you don't get that with thhn/thwn.
And of course Red for positive and black for negative.
Most building departments have not pick up on this yet. But they will.

Aram



    -------- Original Message --------
    Subject: Re: [RE-wrenches] double insulated wire
    From: Will White <[email protected]
    <mailto:[email protected]>>
    Date: Fri, June 28, 2013 10:23 am
    To: RE-wrenches <[email protected]
    <mailto:[email protected]>>

    We use PV Wire which is double insulated on the roof in free air
    and regular THHN/TNWN for the run from the junction box back to
    the inverter (using no white or gray wires of course).
    Thanks,
    Will
    
____________________________________________________________________________________________
    Will White
    Regional Field Operations Manager -- New England
    Real Goods Solar
    64 Main St.
    Montpelier, VT 05602
    Tel: (802) 223-7804
    Cell: (802) 234-3167
    www.realgoodssolar.com <http://www.realgoodssolar.com/>
    *From:*[email protected]
    <mailto:[email protected]>
    [mailto:[email protected]] *On Behalf Of
    *Marco Mangelsdorf
    *Sent:* Friday, June 28, 2013 1:10 PM
    *To:* 'RE-wrenches'
    *Subject:* [RE-wrenches] double insulated wire
    I'm kinda confused.  With more transformerless inverters on the
    market (e.g., SMA and Power-One), it's not clear to me if double
    insulated wiring needs to be used all the way from each series
    string to their respective inverter.
    We've been installing the P1 3-6 kW TL inverters and there's no
    apparent mention of needing to use such conductors, yet I remember
    needing to do so when I installed a number of the 8, 9 and 10 kW
    SMA TL inverters.
    Thanks,
    marco
    ------------------------------------------------------------------------
    _______________________________________________
    List sponsored by Home Power magazine

    List Address: [email protected]
    <mailto:[email protected]>

    Change email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to