Friends:
We used some Bridgeport fittings yesterday. My foreman reports the following: The new blue rain tite connectors have a prob. The connectors have a plastic gasket/ring that seals between the connector body and the box. It is impossible to tighten the con to box without destroying the ring or having a slightly loose con/box connection. A loose connection means poor bonding. I would add that any looseness of these fittings can contribute to mechanical failure of conduit runs. We rely on code compliant strapping *and* secure tightening of fittings to keep a conduit assembly secure and in place for years to come. It looks like we need to find a fitting with firmer washers. The Arlington NMLT fittings have yellow washers that are pretty rigid. I will rob one and try it on the Bridgeports. We bought a quantity of the EMT fittings and I don't want to have to replace them. William From: [email protected] [mailto:[email protected]] On Behalf Of August Goers Sent: Thursday, January 16, 2014 8:00 AM To: RE-wrenches Subject: Re: [RE-wrenches] Concrete tight versus raintight Hi William, About 5 years ago this became a big issue up in San Francisco and we had to learn the hard way. We used to just go buy outdoor EMT fittings and we were okay, then the inspectors started requiring fittings that say raintight or wet location (often stamped "wetloc") on them. I don't know for certain, but I believe it might have been a clarification added in the 2008 NEC at the time. See "NEC 358.42 Couplings and Connectors. Couplings and connectors used with EMT shall be made up tight. Where buried in masonry or concrete, they shall be concretetight type. Where installed in wet locations, they shall comply with 314.15." If you go over to NEC 314.15 they mention that fittings installed in wet locations shall be listed for use in wet locations. So, you just need to make sure that the fittings you get are listed for the correct purpose. I have seen both concretetight and wetloc type. As someone else mentioned, most of the wetloc fittings have a plastic sealing ring in them and many or blue colored. Best, August Luminalt From: [email protected] [mailto:[email protected]] On Behalf Of William Miller Sent: Wednesday, January 15, 2014 10:32 PM To: RE-wrenches Subject: [RE-wrenches] Concrete tight versus raintight Friends: It appears I may have a whole in my education. I thought all EMT compression fittings were alike. It appears that I have been using "concrete tight" fittings where I should have been using "raintight" fittings. Did they use to be the same item? I did a web search on the differences and came up empty. I want to be informed in this area and appreciate any knowledge. William Miller Gradient Cap Lic 773985 millersolar.com <http://www.millersolar.com/> 805-438-5600 _____ No virus found in this message. Checked by AVG - www.avg.com Version: 2013.0.3462 / Virus Database: 3681/7008 - Release Date: 01/16/14
<<image001.jpg>>
_______________________________________________ List sponsored by Home Power magazine List Address: [email protected] Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org