Madison Electric has an actual rubber washer to seal fitting to box as lock 
ring is tightened.  

They are however fussy with the internal rings. 

Erika Weliczko
REpower Solutions
cell: 216.402.4458

On Jan 16, 2014, at 2:54 PM, "William Miller" <[email protected]> wrote:

> Friends:
>  
> We used some Bridgeport fittings yesterday.  My foreman reports the following:
>  
> The new blue rain tite connectors have a prob. The connectors have a plastic 
> gasket/ring that seals between the connector body and the box. It is 
> impossible to tighten the con to box without destroying the ring or having a 
> slightly loose con/box connection. A loose connection means poor bonding.
>  
> I would add that any looseness of these fittings can contribute to mechanical 
> failure of conduit runs.  We rely on code compliant strapping *and* secure 
> tightening of fittings to keep a conduit assembly secure and in place for 
> years to come.  It looks like we need to find a fitting with firmer washers.  
> The Arlington NMLT fittings have yellow washers that are pretty rigid.  I 
> will rob one and try it on the Bridgeports.  We bought a quantity of the EMT 
> fittings and I don’t want to have to replace them…
>  
> William
>  
>  
>  
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of August Goers
> Sent: Thursday, January 16, 2014 8:00 AM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Concrete tight versus raintight
>  
> Hi William,
>  
> About 5 years ago this became a big issue up in San Francisco and we had to 
> learn the hard way. We used to just go buy outdoor EMT fittings and we were 
> okay, then the inspectors started requiring fittings that say raintight or 
> wet location (often stamped “wetloc”) on them. I don’t know for certain, but 
> I believe it might have been a clarification added in the 2008 NEC at the 
> time. See “NEC 358.42 Couplings and Connectors. Couplings and connectors used 
> with EMT shall be made up tight. Where buried in masonry or concrete, they 
> shall be concretetight type. Where installed in wet locations, they shall 
> comply with 314.15.”
>  
> If you go over to NEC 314.15 they mention that fittings installed in wet 
> locations shall be listed for use in wet locations.
>  
> So, you just need to make sure that the fittings you get are listed for the 
> correct purpose. I have seen both concretetight and wetloc type. As someone 
> else mentioned, most of the wetloc fittings have a plastic sealing ring in 
> them and many or blue colored.
>  
> Best,
>  
> August
> Luminalt
>  
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of William Miller
> Sent: Wednesday, January 15, 2014 10:32 PM
> To: RE-wrenches
> Subject: [RE-wrenches] Concrete tight versus raintight
>  
> Friends:
>  
> It appears I may have a whole in my education.  I thought all EMT compression 
> fittings were alike.  It appears that I have been using “concrete tight” 
> fittings where I should have been using “raintight” fittings.  Did they use 
> to be the same item?  I did a web search on the differences and came up 
> empty.  I want to be informed in this area and appreciate any knowledge.
>  
> William Miller
>  
>  
> <image001.jpg>
> Lic 773985
> millersolar.com
> 805-438-5600
>  
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 2013.0.3462 / Virus Database: 3681/7008 - Release Date: 01/16/14
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to