We dialed the inverters back to 3.6 kw charge and got a full bulk and EQ with no breaker trip today. Finally got the SG back up to 1.275 - 1.285 after 4 hours @ 61.5. It had me real nervous for a week, being able to get bulk voltage but still only 1.220 - 1.223 SG.
Now looking at putting in a capacitor bank to correct some of the power factor issues of the inverter/chargers so I can get more useable kw out of the genset.

Thanks for your suggestions!

Bruce Fiero-RMI



Willpower Electric LLC


-------- Original Message --------
Subject: Re: [RE-wrenches] Charging a HUP
From: <[email protected]>
Date: Sun, February 09, 2014 12:04 pm
To: "RE-wrenches" <[email protected]>

Yes Chris. I've got about 42 on one leg and 35-37 on the other. The transformer keeps the legs balanced to within about 5 amps.

Bruce

-------- Original Message --------
Subject: Re: [RE-wrenches] Charging a HUP
From: Chris Mason <[email protected]>
Date: Sun, February 09, 2014 11:13 am
To: RE-wrenches <[email protected]>

So the breaker is not the generator output breaker?
I would put a clamp amp meter on the breaker leads set on Max to record the maximum current when it trips.


On Sun, Feb 9, 2014 at 2:23 PM, <[email protected]> wrote:
True that on the DC genset, Kevin, but more or less removes the bypass option. Strongly considered breaker replacement as many are susceptible to harmonics, but a real PIA on this generator and haven't gotten around to it yet. Also going to run the gen shed ventilators off the line side of the gen when I replace the breaker to avoid overheating when breaker trips!

Bruce
-------- Original Message --------
Subject: Re: [RE-wrenches] Charging a HUP
From: "Kevin Pegg" <[email protected]>
Date: Sun, February 09, 2014 9:39 am
To: "RE-wrenches" <[email protected]>

"Has anybody scoped ac line to VFX's under full charge load? I'm curious about harmonics possibly being the culprit "
 
Yes, it's pretty nasty. This is why we stopped using Outback products for off-grid sites with significant use of generator charging. Not only are the chargers really wimpy, we found all manner of harmonics caused by the charger circuit. Loads ran fine on inverter; fine on generator but would not run at all or reliably with gen running in charge mode.
 
It took some time to figure this out. Ended up having to tear out several new outback systems & replace with another brand to keep customers happy.
 
What we have done successfully for sites where the customer doesn't want to replace the Outback is install a bank of external battery chargers, ie the Iota DLS series and use those for gen charging purposes only. Sub-optimal in a lot of respects but that's what happens when a client buys hardware and says "make it all work". A DC genset would be way more efficient.
 
Another thought have you tried another breaker on the gen? Weak breakers do happen, have seen that on brand new gensets.
 
Kevin
-----Original Message-----
From: [email protected] [mailto:[email protected]]On Behalf Of [email protected]
Sent: February 9, 2014 9:28 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Charging a HUP

Roger the 136-272 charge amps, and the theoretical max of 295 with this system. Hoping for reality of 160 - 200. Fortunately it's a 'good' customer with very efficient running loads, just a bit of a power tool habit and the hydronic heating recirc pump loads. Unfortunately, there have been 3 trades on site recently using power while I'm trying to get the battery filled up! but generally about 3x solar/useage during fair weather.
With 3 inverters, this week I'm trying #3 with full charging, 1 and 2 at about 60%. #1 should carry most of the load demands, #3 most of the charge demand. I also found a spot in the Mate 3 to set maximum charging kw and I set that to 7kw. Maybe that will help gen overload.
Has anybody scoped ac line to VFX's under full charge load? I'm curious about harmonics possibly being the culprit between a 12.3 kw load bank not tripping the breaker, and a 5-6 kw charging load tripping the breaker...

Bruce

-------- Original Message --------
Subject: Re: [RE-wrenches] Charging a HUP
From: "RE Ellison" <[email protected]>
Date: Sun, February 09, 2014 8:07 am
To: "'RE-wrenches'" <[email protected]>

Thanks Jay,
We used to be able to figure the max charge rate at 25% of the packs capacity. That might not work with the HUP packs.
Glad you have a manual!
It is always a good idea to follow the directions in the manuals!
Later,
Bob Ellison
From: [email protected] [mailto:[email protected]] On Behalf Of jay peltz
Sent: Sunday, February 09, 2014 9:38 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Charging a HUP
Hi guys,
The HUP manual specifies minimum charge rate of 136 amps, max at 272,
jay
peltz power
On Feb 9, 2014, at 1:38 AM, RE Ellison wrote:


Sounds like there is a need for a bigger generator, my gut tells me there is almost enough (but not quite), with 12kw to almost max the chargers and nothing left to feed the other loads.
I have found that “on paper” and reality do not always mix well.
Getting max theoretical charging capacity from solar and the generator at the same time is sometimes a tough nut to crack, although batteries seem to “like” the varying charge better than a steady max charge. That battery can probably absorb 420 amps as the charging max using the usual 3 stage charging we have with inverters, you’re not getting anywhere near enough to max them with that generator. Powering down all the chargers 30% or so (or 1 inverter totally) would help stop the breaker trips but slow the charging off the generator. Then you just need to pray for lots of sun.
Is the solar alone enough to power the loads in the normal day to day usage in a best case situation, or is this a case of the generator has to run to keep up?
Up here we have seen 1 sunny day in 3 weeks, we know about generator usage…..
I can’t speak on the HUP’s. I have never used them, but might they be somewhat hard to charge?
Just some thoughts, but it’s 3 am and I hope it makes sense in the morning when I reread it….
Later,
Bob
From: [email protected] [mailto:[email protected]] On Behalf Of [email protected]
Sent: Sunday, February 09, 2014 1:29 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Charging a HUP
Hi Larry,
I have an FNDC in the system. Manufacturer wanted 2 hour EQ before adding water to the new battery. We got that and had SG between 1.260 and 1.275 on all 24 cells. Cells were very thirsty (shipped with electrolyte almost to the plates) and took 8.5 gallons between all cells. We aren't having much trouble getting voltage back up but SG is below 1.23 (within .01 on cells tested). Strategy at this point is to give a daily bulk and absorb and EQ every 3 or 4 days for extended times and monitor SG. Discontinue hard charging when SG plateaus. I generally shoot for c/10 charge current, and nervous about barely c/20 and a 12kw genset only giving me about 5.
Bruce
-------- Original Message --------
Subject: Re: [RE-wrenches] Charging a HUP
From: "Larry Crutcher, Starlight Solar Power Systems"
<[email protected]>
Date: Sat, February 08, 2014 11:50 am
To: RE-wrenches <[email protected]>

Hi Bruce,
Please explain "feeding it properly". Charging any lead acid battery slowly actually preserves battery life. As long as you are achieving the recommended charge voltage (temperature compensated) for long enough time, and reaching 100% SoC regularly, you are caring for the battery.
At 82kWh battery capacity and 6.5kW PV, the customer may have a hard time getting to 100%. You did not mention, but I HOPE you have a battery capacity meter in the system. It's mandatory if they want to care for the battery. Since the customer has a small generator, they need to realize the limitations and reduce their loads during generator time so you can use the full output.
Larry
On Feb 7, 2014, at 11:46 PM, [email protected] wrote:
Hi All,
3 VFX 3648
2 FM 80
6.5 kw solar
12 kw generator
PSX 240 on generator output and VFX stacking
Mate 3
HUP 1690 ah
System design considering 45 amp charge current from each VFX totaling 135 amps. (135 x ~55v = 7.42kw)  Potential charge current from 2 arrays and FM 80's, 90 - 100 amps. On a good day, reasonable to expect 200+ amps?
Have not been able to exceed 90 amps for more than 30 minutes, with the generator putting out about 9 kw before it's 70 amp 2pole breaker trips. L1 42 amps, L2 37 amps. 5 amps neutral. Load banked to 12.3 kw (51 amps @ 240v) resistive without breaker trip.
I have had to dial back the maximum charge current in the Mate 3 to 12 amps each on two of the inverters (L1 and L2) and 8 on inverter 3 to keep the generator from tripping out when customer turns on the microwave or coffee pot. In effect, 42 amps charge @ 240 v = 7.6 kw. At the battery, I'm only seeing 80 amps of charge current. Running loads are typically less than 1 kw but there has been a of construction going on with chop saws and compressors creating annoying spikes that are easily handled by the inverters when the generator is off.
I don't want to kill this new battery by not feeding it properly! I would have put in a larger generator, but the owner bought the 12 kw before deciding on the new battery. I thought the 12 would be merely adequate, but not so....
Any suggestions?
Thanks!
Bruce Fiero-RMI



<sigimg0.jpeg>



No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4259 / Virus Database: 3697/7076 - Release Date: 02/08/14

No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4259 / Virus Database: 3697/7076 - Release Date: 02/08/14

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





--
Chris Mason
President, Comet Systems Ltd
Cell: 264.235.5670
Skype: netconcepts

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to