Hey guys,

The FX's have always been rough to generator waveforms, back some 9-10 years 
ago there was a case in Alaska that identified that they (FX's) don't play well 
with capacitive coupled regulators.  We brought in several generators and the 
guys in engineering worked on a fix but never found one other than a $500.00 
dollar tank circuit filter that most of the time didn't work.

At that point anything with a capacitive coupled regulator would have to be 
backed way off, and would cause a really nasty flicker of the Lights/loads when 
the inverter was charging the battery bank.

Electronically regulated regulators work better, but the way the inverter 
measures ac input amperage can also be way off.  I've seen the metering display 
7 amps when indeed the actual current pull was closer to 10-11 amps.   This is 
most often the cause of the mystery breaker tripping.

One of the things I always did that worked pretty well was.

Turn the charge rates down to zero.
Start the Genset, wait till connection.
Edge the charge rates up 1 amp at a time to see how much the genset can handle.

I've usually found that at about 60-70% of the rated current is where the sweet 
spot is.

Another issue that I've seen come up affect multiple stacks of inverters 
regardless of their manufacture.  Most inverter/chargers in this market are 
Voltage Controlled chargers.  This means that current follows voltage, if 
voltage is low then current is high... once voltage get to say Absorb voltage 
the combination of the inverter seeing the absorb voltage and the battery no 
longer is accepting max current the amount of current flowing drastically 
drops.   This tends to drive customers/installers crazy on how to maximize the 
amount of current flowing into the battery.  Remember, once you get past the 
Bulk Charging stage you cannot force current into a battery, it's only going to 
accept what it can.

A secondary issue to this is when you have multiple chargers connected to the 
same battery bank. Very often if you have a quad stack of Outback's you will 
see on or two inverters charging while the rest of the inverters are sleeping, 
this is normal as nobody's products to my knowledge share charging information 
that will equally divide charging current between the sources.

Just something else to chew on.... Altitude will also affect how well the 
generator operates, as the higher you go the thinner the air the less 
efficiently the fuel burns.


Steve Higgins
Technical Services Manager
P: 800.681.9914
M: 206.790.5840
F: 902.597.8447
Surrette Battery Company

http://www.rollsbattery.com

Steve Higgins
Technical Services Manager
M: +1.206.790.5840
F: +1.902.597.8447
Surrette Battery Company
Exclusive manufacturer of

________________________________________
From: [email protected] 
[[email protected]] on behalf of Doug Wells 
[[email protected]]
Sent: Tuesday, February 11, 2014 11:03 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Outback Chargers

Kevin,

I am curious about what you are seeing on the Outbacks as well.
Have dozens of these out in the field.  They have been pretty reliable for me.
The biggest issue that I have had with them is when the inverters are 
transferring from generator charging back to inversion.
If you leave this at the factory default, 1 s, you will see light flicker, and 
sensitive electronics will go into error.
This transfer rate can be adjusted down and has cured most of the power quality 
issues with the battery charging.
A different issue than harmonics under load, but it might help.

Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com



_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




This email and its attachments have been scanned by iConnection E-Mail Firewall 
for viruses, spam, and malicious content.
The information transmitted in this email is intended only for the entity or 
person to which it is addressed and may contain confidential/privileged 
material. If you received this in error, please contact the sender and delete 
the material from any computer. Any review, retransmission, dissemination, or 
other use of this information by persons or entities other than the intended 
recipient is strictly prohibited. %^^%
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to