AutoCad can indeed be a tricky platform, when I learned how to use it I found 
an inexpensive tutor for about two days over the computer using a screen share. 
It was probably some of the best of the money I have ever spent. 

Jason D. Kechijian, LEED AP BD+C
NABCEP Certified PV Installation Professionalâ„¢
NABCEP Certified PV Technical Sales Professionalâ„¢ 
[email protected]
(843) 200-7271

On Mar 13, 2014, at 1:43 PM, [email protected] wrote:

> Send RE-wrenches mailing list submissions to
>       [email protected]
> 
> To subscribe or unsubscribe via the World Wide Web, visit
>       http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
> or, via email, send a message with subject or body 'help' to
>       [email protected]
> 
> You can reach the person managing the list at
>       [email protected]
> 
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of RE-wrenches digest..."
> 
> 
> When responding to posts within the Digest, be sure to restore the Subject: 
> line to the original, and please edit out any extraneous lines from the 
> quoted message.
> 
> 
> Today's Topics:
> 
>   1. Re: Autocad (Jerry Shafer)
>   2. Re: Autocad (Mac Lewis)
>   3. Re: Autocad (Solarguy)
>   4. Re: AC Combiner with main breaker as system disconnect
>      (Mark Richardson)
>   5. Re: Huge battery bank recommendation (Kevin Pegg)
> 
> 
> ----------------------------------------------------------------------
> 
> Message: 1
> Date: Wed, 12 Mar 2014 20:56:18 -0700
> From: Jerry Shafer <[email protected]>
> To: RE-wrenches <[email protected]>
> Subject: Re: [RE-wrenches] Autocad
> Message-ID:
>       <CAMUFgmWHGifDPnHScDPX1uqEo4zTbCXKAD7HDDu-VzA4b=d...@mail.gmail.com>
> Content-Type: text/plain; charset="iso-8859-1"
> 
> Some state schools teach auto cad and of you are in the class learning the
> application you can get a student version for free
> Jerry
> On Mar 12, 2014 4:09 PM, "William Miller" <[email protected]> wrote:
> 
>> Friends:
>> 
>> 
>> 
>> The 3D CAD software I have been using is obsolete.  I have decided to
>> upgrade to Autocad.  I am temporarily using an educational copy while I
>> learn, but  I need to purchase a copy.
>> 
>> 
>> 
>> Before I go out and plunk down $4k, I need to do some research:
>> 
>> 
>> 
>> Do I have to expect to pay that much?
>> 
>> 
>> 
>> Where is a good place to purchase?
>> 
>> 
>> 
>> Are there copies of one generation old programs available?
>> 
>> 
>> 
>> I am a self teacher but I use printed texts.  What is your favorite
>> Autocad reference?
>> 
>> 
>> 
>> Thanks everyone!
>> 
>> 
>> 
>> William
>> 
>> 
>> 
>> 
>> 
>> [image: Gradient Cap_mini]
>> 
>> Lic 773985
>> 
>> millersolar.com (hyperlink)
>> 
>> 805-438-5600
>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: [email protected]
>> 
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
>> 
>> 
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140312/e7e8e456/attachment.html>
> -------------- next part --------------
> A non-text attachment was scrubbed...
> Name: image001.jpg
> Type: image/jpeg
> Size: 1460 bytes
> Desc: not available
> URL: 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140312/e7e8e456/attachment-0001.jpg>
> 
> ------------------------------
> 
> Message: 2
> Date: Wed, 12 Mar 2014 22:39:37 -0600
> From: Mac Lewis <[email protected]>
> To: RE-wrenches <[email protected]>
> Subject: Re: [RE-wrenches] Autocad
> Message-ID:
>       <caoabg483psgyaa3ty5r46d-z5xb4od1wkuy8jomqb_6bm45...@mail.gmail.com>
> Content-Type: text/plain; charset="iso-8859-1"
> 
> Hi William,
> 
> One thing I have found with AutoCad is that it helps to start with
> something.  A big blank model space is an intimidating place with nothing
> in it.  If you do end up getting it, shoot me an email and I'll share some
> dwgs that may help by giving you some building blocks.  I will mention
> however, that I just do 2D with AutoCad and use Sketchup (Free Version) for
> 3D, so it may not be a big help.
> 
> Good Luck
> 
> 
> On Wed, Mar 12, 2014 at 9:56 PM, Jerry Shafer <[email protected]>wrote:
> 
>> Some state schools teach auto cad and of you are in the class learning the
>> application you can get a student version for free
>> Jerry
>> On Mar 12, 2014 4:09 PM, "William Miller" <[email protected]> wrote:
>> 
>>> Friends:
>>> 
>>> 
>>> 
>>> The 3D CAD software I have been using is obsolete.  I have decided to
>>> upgrade to Autocad.  I am temporarily using an educational copy while I
>>> learn, but  I need to purchase a copy.
>>> 
>>> 
>>> 
>>> Before I go out and plunk down $4k, I need to do some research:
>>> 
>>> 
>>> 
>>> Do I have to expect to pay that much?
>>> 
>>> 
>>> 
>>> Where is a good place to purchase?
>>> 
>>> 
>>> 
>>> Are there copies of one generation old programs available?
>>> 
>>> 
>>> 
>>> I am a self teacher but I use printed texts.  What is your favorite
>>> Autocad reference?
>>> 
>>> 
>>> 
>>> Thanks everyone!
>>> 
>>> 
>>> 
>>> William
>>> 
>>> 
>>> 
>>> 
>>> 
>>> [image: Gradient Cap_mini]
>>> 
>>> Lic 773985
>>> 
>>> millersolar.com (hyperlink)
>>> 
>>> 805-438-5600
>>> 
>>> 
>>> 
>>> _______________________________________________
>>> List sponsored by Home Power magazine
>>> 
>>> List Address: [email protected]
>>> 
>>> Change email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive:
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out participant bios:
>>> www.members.re-wrenches.org
>>> 
>>> 
>>> 
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: [email protected]
>> 
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
>> 
>> 
> 
> 
> -- 
> 
> 
> 
> Mac Lewis
> 
> *"Yo solo s? que no s? nada." -S?crates*
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140312/2c8ca6d8/attachment-0001.htm>
> -------------- next part --------------
> A non-text attachment was scrubbed...
> Name: image001.jpg
> Type: image/jpeg
> Size: 1460 bytes
> Desc: not available
> URL: 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140312/2c8ca6d8/attachment-0001.jpg>
> 
> ------------------------------
> 
> Message: 3
> Date: Thu, 13 Mar 2014 08:14:36 -0500
> From: "Solarguy" <[email protected]>
> To: "'RE-wrenches'" <[email protected]>
> Subject: Re: [RE-wrenches] Autocad
> Message-ID: <[email protected]>
> Content-Type: text/plain; charset="us-ascii"
> 
> A correction to my earlier reply: 
> 
> AutoCad will 'print' directly to a pdf file on newer versions using MS
> Windows7 & 8. Adobe no longer supports that function on earlier versions of
> Acad. Mine is a full commercial version of 2000i and works flawlessly today.
> 
> 
> In the 80s & 90s text & other instructional books came with all software.
> Find old copies, often 100s of pages of commands & examples. Acad doesn't
> ever change commands, just adds new ones so even a decade old book is
> accurate. 
> 
> Find a local chapter of an AutoCad Users Group to meet others with decades
> of knowledge.
> 
> 
> 
> Jim Duncan
> 
> 
> 
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Bill Brooks
> Sent: Wednesday, March 12, 2014 6:34 PM
> To: 'RE-wrenches'
> Subject: Re: [RE-wrenches] Autocad
> 
> 
> 
> William,
> 
> 
> 
> Go to  http://www.associatedsoftwaresales.com/home.php . They do a 48-month
> lease of 2013 AutoCAD LT for $325. If you really need AutoCAD, there is no
> cheaper route that I know of.
> 
> 
> 
> Bill.
> 
> 
> 
> 
> 
> From: [email protected]
> [mailto:[email protected]] On Behalf Of William
> Miller
> Sent: Wednesday, March 12, 2014 4:09 PM
> To: RE-wrenches
> Subject: [RE-wrenches] Autocad
> 
> 
> 
> Friends:
> 
> 
> 
> The 3D CAD software I have been using is obsolete.  I have decided to
> upgrade to Autocad.  I am temporarily using an educational copy while I
> learn, but  I need to purchase a copy.
> 
> 
> 
> Before I go out and plunk down $4k, I need to do some research:
> 
> 
> 
> Do I have to expect to pay that much?
> 
> 
> 
> Where is a good place to purchase?
> 
> 
> 
> Are there copies of one generation old programs available?
> 
> 
> 
> I am a self teacher but I use printed texts.  What is your favorite Autocad
> reference?
> 
> 
> 
> Thanks everyone!
> 
> 
> 
> William
> 
> 
> 
> 
> 
> Gradient Cap_mini
> 
> Lic 773985
> 
> millersolar.com (hyperlink)
> 
> 805-438-5600
> 
> 
> 
> 
> 
>  _____  
> 
> 
> <http://www.avast.com/> 
> 
> This email is free from viruses and malware because avast! Antivirus
> <http://www.avast.com/>  protection is active. 
> 
> 
> 
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140313/97a9d4b9/attachment-0001.htm>
> -------------- next part --------------
> A non-text attachment was scrubbed...
> Name: not available
> Type: image/jpeg
> Size: 1460 bytes
> Desc: not available
> URL: 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140313/97a9d4b9/attachment-0001.jpeg>
> 
> ------------------------------
> 
> Message: 4
> Date: Thu, 13 Mar 2014 16:08:20 +0000
> From: Mark Richardson <[email protected]>
> To: RE-wrenches <[email protected]>,
>       "[email protected]"  <[email protected]>
> Subject: Re: [RE-wrenches] AC Combiner with main breaker as system
>       disconnect
> Message-ID:
>       <[email protected]>
> Content-Type: text/plain; charset="utf-8"
> 
> Hi All,
> Just wondering if someone could confirm or expand on the assertion in Jason?s 
> document that:
> ?NEC Article 690.64(A) allows a Line?Side AC connection to busbars, 
> conductors, or lugs at any
> point between the customer?s side of the utility meter, and the service 
> disconnect. Many folks
> call this a ?line?side tap?, which leads to confusion with the ?10?foot tap 
> rule? and Article
> 240.21(B). Tap rules and Article 240 do not apply here (emphasis added). 
> These aren?t feeders, and service
> entrance cables don?t have overcurrent protection?
> Our engineers and design teams have always considered the Tap rules (Article 
> 240, et al.) when utilizing a supply/line side connections and the utility 
> here looks at this as a ?separately derived service.?
> Thanks,
> Mark Richardson
> US Light Energy
> 
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Bill Brooks
> Sent: Wednesday, March 12, 2014 8:13 PM
> To: [email protected]; 'RE-wrenches'
> Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect
> 
> Glenn,
> 
> It may be that the equipment sold in your region is that way, but my 
> experience is the opposite. I just looked in my electrical service panel at 
> my home to check my sanity and it is 10,000A rated. So is every single-phase 
> breaker sold at Home Depot or Lowes. You can?t put 10k breakers in a 
> 25,000AIC panel unless you know the fault current is under 10kA.
> 
> I can?t argue with what you see, but you may be misinterpreting the ratings 
> on the equipment. You may be reading something on the actual breaker, but 
> that does not mean that it is 20kAIC in the panel. It has to be tested and 
> listed with the panel. Again, the key is to confirm what the rating of the 
> panel is. That is located on the inside cover or you can get that from the 
> manufacturer.
> 
> Bill.
> 
> 
> From: 
> [email protected]<mailto:[email protected]>
>  [mailto:[email protected]] On Behalf Of Glenn Burt
> Sent: Wednesday, March 12, 2014 4:51 PM
> To: 'RE-wrenches'
> Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect
> 
> Bill,
> 
> I have never seen a main breaker in a residential main load center (say 200A) 
> that has a rating of less than 20k AIC. Is there somewhere else in the panel 
> that changes this?
> 
> Glenn
> 
> From: 
> [email protected]<mailto:[email protected]>
>  [mailto:[email protected]] On Behalf Of Bill Brooks
> Sent: Wednesday, March 12, 2014 7:24 PM
> To: 'RE-wrenches'
> Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect
> 
> Glenn,
> 
> The vast majority of service equipment for residences is rated 10k AIC. 
> Although utilities may say they have some residential services that exceed 
> 10k short circuit availability, it is still pretty rare.
> 
> Using single phase gear on a 3-phase commercial installation is a different 
> story. Perhaps this is what you were referring to when talking about 10k AIC 
> being too low.
> 
> I don?t people to get the idea that you have to check the fault current of 
> every PV installation. You should only have to check fault current on a new 
> service. Simply checking the ratings of the exist service equipment at an 
> installation is sufficient to know what the minimum AIC rating of the 
> equipment must be. The utility is not legally allowed to increase the fault 
> current on a service above the service equipment ratings unless it is part of 
> a service upgrade and the service equipment is being replaced.
> 
> Bill.
> 
> 
> From: 
> [email protected]<mailto:[email protected]>
>  [mailto:[email protected]] On Behalf Of Glenn Burt
> Sent: Wednesday, March 12, 2014 3:13 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect
> 
> Beware of breakers used as service disconnects. Most in the range suitable 
> for a supply side connections for PV are really branch circuit rated with 10k 
> AIC which is generally too low for the utility fault current they may be 
> exposed to.
> If you can get a statement from the utility with available fault current at 
> the install site you might sneak one in. If you don't want to go to this 
> trouble, use the rating of the exiting main breaker as a minimum value. 
> Usually 20-25k AIC.
> ________________________________
> From: Brian Teitelbaum<mailto:[email protected]>
> Sent: ?3/?12/?2014 17:32
> To: RE-wrenches<mailto:[email protected]>
> Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect
> One big omission, in the otherwise fine Soligent white paper, is that the 60A 
> minimum disconnect has to be rated as ?Service Equipment?. Generally this 
> means a ?Heavy-Duty? safety switch or Service-rated load center with Main 
> breaker.
> 
> I don?t see why an AC breaker panel, with a Main breaker, couldn?t act as the 
> PV system disconnect, as long as it?s Service-rated, a minimum of 60A, and 
> the utility does not require an external-handle disconnect, lockable in the 
> off position. Many utility companies still do.
> 
> Brian Teitelbaum
> AEE Solar
> 
> 
> 
> From: 
> [email protected]<mailto:[email protected]>
>  [mailto:[email protected]] On Behalf Of Jason 
> Szumlanski
> Sent: Wednesday, March 12, 2014 2:14 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect
> 
> Don't utter the word tap. :)
> 
> See:
> http://www.soligent.net/documents/HappyLandings_v3.pdf
> 
> We usually specify a fusible disconnect for overcurrent protection when 
> grouping the PV AC combiner with the main premises disconnect is not 
> practical.
> 
> 
> Jason Szumlanski
> Fafco Solar
> 
> 
> 
> 
> On Wed, Mar 12, 2014 at 1:31 PM, 
> <[email protected]<mailto:[email protected]>> wrote:
> I am trying to determine whether an AC combiner panel (for multiple inverter 
> outputs) with main breaker can be also used as the PV system disconnect?
> 
> This is for a line tap situation.  I am accustomed to doing these systems 
> with an AC combiner, and separate enclosure for a breaker style, line tap 
> over current protection.
> 
> Any thoughts/comments would be appreciated.
> 
> Thanks,
> 
> Kevin
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: 
> [email protected]<mailto:[email protected]>
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
> 
> Check out participant bios:
> www.members.re-wrenches.org<http://www.members.re-wrenches.org>
> 
> 
> ________________________________
> [http://static.avast.com/emails/avast-mail-stamp.png]<http://www.avast.com/>
> 
> 
> This email is free from viruses and malware because avast! 
> Antivirus<http://www.avast.com/> protection is active.
> 
> 
> 
> ________________________________
> [http://static.avast.com/emails/avast-mail-stamp.png]<http://www.avast.com/>
> 
> 
> This email is free from viruses and malware because avast! 
> Antivirus<http://www.avast.com/> protection is active.
> 
> 
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140313/0252ec4f/attachment-0001.htm>
> 
> ------------------------------
> 
> Message: 5
> Date: Thu, 13 Mar 2014 10:31:22 -0700
> From: "Kevin Pegg" <[email protected]>
> To: "RE-wrenches" <[email protected]>
> Subject: Re: [RE-wrenches] Huge battery bank recommendation
> Message-ID:
>       <[email protected]>
> Content-Type: text/plain; charset="iso-8859-1"
> 
> Hi Mac, 
> 
> We fabricated and operate a similar sized (400 kWh) battery / inverter / 
> generator hybrid system for BC Hydro, our power utility servicing a remote 
> community. It has been online for 2 years now. 
> 
> Using Dekka / East Penn D-series batteries which we had custom built to our 
> specs. 
> 
> A notable difference is we have 100 kW diesels and 60 kW inverter capacity in 
> a 120/208 SMA inverter config (stepped up to 14.4 kV distribution). The 
> system works really well and it currently 100% uptime for last 12 months. 
> This is an unattended system we are onsite to maintain every 2 months. No 
> renewable input at this time. 
> 
> The sizing you have reported seems out of ratio. ~ 20 kW of charging power 
> into a 400 kWh battery bank ie C/5. Depending on the loads the gen is 
> carrying along with charging that could further reduce available charge 
> capacity. That generator is going to have to run for a very long time to 
> charge that battery. We call this the big battery blunder syndrome - which 
> has caused many failures of such scale of system. 
> 
> Kevin
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]]On Behalf Of Mac Lewis
> Sent: March 11, 2014 7:27 AM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Huge battery bank recommendation
> 
> 
> To clarify, this is for an off-grid application, 4 Sunny Islands, 30kW 
> generator.
> 
> 
> On Tue, Mar 11, 2014 at 9:16 AM, August Goers < [email protected]> wrote:
> 
> 
> Mac, 
> 
> Is this for an off grid system? We're doing our first project with a Deka 
> Unigy II battery system but they are AGM and I believe only good for grid 
> tied battery backup or applications where you won't have a very deep depth of 
> discharge:
> 
> http://www.dekabatteries.com/assets/base/0919c.pdf
> 
> 
> Best,
> 
> August
> 
> 
> August Goers
> 
> Principal
> 
> Luminalt Energy Corporation
> 
> o: 415.641.4000
> 
> m: 415.559.1525
> 
> www.luminalt.com
> 
> 
> 
> 
> 
> On Tue, Mar 11, 2014 at 6:24 AM, Mac Lewis < [email protected]> wrote:
> 
> 
> Hi wrenches, 
> 
> I am consulting on a job that requires an 8000 Ahr battery bank.  This is 
> quite a bit beyond my normal battery bank realm.  What would you recommend 
> for this?
> 
> Thanks in advance
> 
> 
> -- 
> 
> 
> 
> 
> 
> Mac Lewis
> 
> 
> 
> "Yo solo s? que no s? nada." -S?crates
> 
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
> 
> 
> 
> 
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
> 
> 
> 
> 
> 
> 
> -- 
> 
> 
> 
> 
> 
> Mac Lewis
> 
> 
> 
> "Yo solo s? que no s? nada." -S?crates
> 
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140313/f5977e96/attachment-0001.htm>
> 
> ------------------------------
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
> 
> 
> End of RE-wrenches Digest, Vol 7, Issue 110
> *******************************************

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]