I had a nice response all typed up before rediscovering my original source. Simple answer: there's still a thermal load to deal with even though there's no point on the bus seeing a current above the busbar rating. I am a linking machine today:
http://www.nmsu.edu/~tdi/Photovoltaics/Codes-Stds/690.64(B)(2)Load%20Side%20Connections.pdf

/While this situation of connecting supply overcurrent devices at opposite ends may be // //safe for restricted conductors, it may not be suitable for busbars in panel boards, even // //though this allowance is in the 2008 NEC. Panel boards are subject to busbar current // //limitations and are also subject to thermal limitations due to the heating associated with // //the thermal trip elements in the common thermal/magnetic molded case circuit breakers. // //For example a 100-amp, 120/240V panel board is tested during the listing process with a // //100 amp main breaker and two 100-amp load breakers (one per phase) mounted directly // //below the main breaker. The ambient temperature is raised to 45 degrees Celsius, the // //input and output currents are set at 100 amps, the temperature is allowed to stabilize, // //and the panel must pass this test with no deformation of any parts. If we add a backfed // //PV breaker pair, for example 50 amps, at the bottom of the panel, and if the loads on the // //panel were increased to 150 amps, no breakers would trip, no busbars would be over // //loaded, but the thermal load in the panel would be that associated with 300 amps, not the // //200 amps the panel was designed and listed for. Panel manufacturers have stated that // //these panels cannot pass UL listing tests with those excessive thermal loads./

On 2014/3/27, 14:34, Troy Harvey wrote:
I am wondering about the busbar 120% rule, and if there is any wiggle room in the 2014 NEC.

Fundamentally I don't understand the 120% rule. If my solar breaker is installed properly at the bottom of the busbar, and the grid-tie breaker is installed at the top, and the busbar itself is rated for 120% of the panel rating, I don't see any means by which a solar breaker of a size substantially larger than 120% could cause a problem. There can be no place on the busbar under any situation (that I can think of) that would exceed 120% because the supply current is coming from opposite ends of the bus bar - even in the worst case load situation. So even if I had a huge PV system (100A), backfeeding the bottom of a 200A panel, I don't see a situation where there is more than 200A over any one section of busbar. Am I wrong, or is the NEC just too prescriptive for its own good?

Also would you say that the 120% is based on the inverter max output or backfeed breaker size?


thanks,

Troy Harvey
---------------------
Principal Engineer
Heliocentric
801-453-9434
[email protected] <mailto:[email protected]>





_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to