Here's an off list reply from a friend of mine at SMA:
Sunny islands are alive and well in the US.
SMA required distributors to technically support them to get the best pricing.
Some of the big boys declined and have been eliminating their advanced tech
support, design services.
Who told you SI-US is going away?
To "stack" 3 phase clusters you use a multicluster box. You can gang 12 si's
that way.
-Wes
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 3/24/2014 10:41 PM, [email protected] wrote:
Ray:
Sunny Islands being discontinued: Did not know that!
XW inverters: Not impressed and have had mixed results. I have resolved
most issues but dealt with glitchy, overcomplicated software and firmware.
Some are reluctant to connect to generators and earlier firmware would not
sell efficiently. Also the BOS cabinet is way too small, but aren't they
all?
Wm
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ray Walters
Sent: Monday, March 24, 2014 8:35 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] 208 3 phase Off Grid Inverter
Hi William;
I was told by two different major distributors a few months ago that the
Sunny Islands were not going to be available in the US anymore
because of some volume purchasing issues. Has that been sorted out?
The XW I have not installed, since I've had poor results with other recent
Schneider products. No where could I find in the spec sheet any mention of
3 phase/ 208 capability, but I found some mention of 3 phase in the manual
for the XW Config software. (XW 6048 Spec sheet just says single phase, so
is this a newer capability? or just in the config software) Do you have
specs or a wiring diagram for the XW in 208/ 3 phase? For instance, what is
the L to L (single phase) power rating at 208 vac?
Are the XWs decent? I've heard some positive feed back from other wrenches.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 3/24/2014 8:58 PM, William Miller wrote:
Ray
Sunny Island or XW.
Wm
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ray
Walters
Sent: Monday, March 24, 2014 7:44 PM
To: RE-wrenches
Subject: [RE-wrenches] 208 3 phase Off Grid Inverter
Hi All;
I'm exploring options for an off grid project with an existing 30 Kw
Kohler wired for 208 vac 3 phase. The generator runs some 8 hp air
compressors, so rewiring it is not an option. We're primarily
interested in reducing gen run time from the current situation: 14 hrs/
day.
So far, only the Outback VFX inverters seem capable of being wired in
208, 3 phase, but according to the manual they can only be stacked 1
inverter per leg. This limits the system to only 3 inverters total, or
10.8 kW. I would like expandability beyond this.
1) are there any other inverters available that I'm over looking?
2) Should I consider a transformer to convert from 208 vac/3phase to
240 vac/ singe phase?
We're not going to even try to run the compressors, just the other
single phase loads, mostly 120 vac, but we have a couple of small air
conditioners, that are currently running on 208 single phase. I
believe they would run fine on 240 vac, as they have a name plate rating
at 230 vac.
3) We may possibly run 2 separate 3 inverter stacks and only tie
together at the battery, but otherwise they would not be connected.
This seems inefficient, and would require some load balancing of the
various inverters.
All help and discussion is greatly appreciated as always,
--
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: [email protected]
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org