Read 690.9(D) and 690.34. Not sure where this "hysteria-run for the border"
sentiment is coming from.

 

690.9(D) Photovoltaic Source and Output Circuits. Listed PV

overcurrent devices shall be required to provide overcurrent

protection in PV source and output circuits. The overcurrent

devices shall be accessible but shall not be required to

be readily accessible.

 

690.34 Access to Boxes. Junction, pull, and outlet boxes

located behind modules or panels shall be so installed that

the wiring contained in them can be rendered accessible

directly or by displacement of a module(s) or panel(s) secured

by removable fasteners and connected by a flexible

wiring system.

 

This is not a change. Please help me understand the concern.

 

Bill Brooks.

 

 

From: [email protected]
[mailto:[email protected]] On Behalf Of Ray Walters
Sent: Monday, April 28, 2014 2:23 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] (no subject)

 

Interesting so does "require a tool" include taking a screw off the cover
plate of the combiner box, too?
What a game changer.  I'm going to Mexico for my next project; I'll actually
enjoy even more being the sole AHJ on the project.  



R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/28/2014 2:52 PM, Michael Morningstar wrote:

Readily accessible is now defined in the 2014 NEC. Installing OCPD's
underneath a module is a major faux paux, and I can't imagine any AHJ
thinking otherwise. Having to remove a module in order to reset a breaker,
what a drag.

 

"Capable of being reached quickly for operation, renewal or inspection
without requiring those concerned to use a tool, to climb over, remove
obstacle or other."

 

Michael

 

 

 





On Apr 28, 2014, at 10:29 AM, William Miller <[email protected]
<mailto:[email protected]> > wrote:





You call it a solar panel, I call it a glass j-box cover plate. 

William

Miller Solar




On Apr 28, 2014, at 9:21 AM, Jason Szumlanski <[email protected]
<mailto:[email protected]> > wrote:

If that is the interpretation,
I don't see how the breakers are "readily accessible" in a SolaDeck
mounted anywhere, regardless of whether it is under a module. It
requires removal of four screws (using a tool) to access the breakers
inside the enclosure. It's all up to the AHJ. It has not been an issue
locally here. I can see how other jurisdictions may not
concur.

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]
<mailto:[email protected]> 

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>


Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org> 

 






_______________________________________________
List sponsored by Home Power magazine
 
List Address: [email protected]
<mailto:[email protected]> 
 
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>

 
Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org> 
 

 



---
This email is free from viruses and malware because avast! Antivirus protection 
is active.
http://www.avast.com
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to