I think 240.24(A)(4) allows the installation of the inverter OCPDs in the SolaDeck hidden under a module.

** *240.24 Location in or on Premises.*
** National Electrical Code 2008 Edition *(A) Accessibility.* Overcurrent devices shall be readily accessible and shall be installed so that the center of the grip of the operating handle of the switch or circuit breaker, National Electrical Code 2008 Edition when in its highest position, is not more than 2.0 m (6 ft 7 in.) above the floor or working platform, unless one of the following applies:
...
(4) For overcurrent devices adjacent to utilization equipment that they supply, access shall be permitted to be by portable means.


And if panelboards / fused safety switches are allowed to have screwed-down covers over the OCPDs, I'd think that installing a removable module over these OCPDs would meet NEC. I guess an AHJ could argue that this requires TWO covers be removed, unlike a panelboard or a switch.

DKC


On 2014/4/29, 11:15, Jason Szumlanski wrote:
690.9(D) is not applicable to the original discussion because we were talking about an Inverter output circuit, not a PV Source or Output circuit.

690.34 may apply if you call a SolaDeck with breakers a junction box, but I can see that being a stretch in the mind of many.

My and Ray's question about the screws on the SolaDeck cover itself requiring a tool to render it accessible is still an issue if the breakers themselves need to be "readily accessible," but that would also apply to a Midnite MNPV, which also has a cover with a screw.


Jason Szumlanski


    On 4/28/2014 5:57 PM, Bill Brooks wrote:

    Read 690.9(D) and 690.34. Not sure where this "hysteria---run for
    the border" sentiment is coming from.

    *690.9(D) Photovoltaic Source and Output Circuits. *Listed PV

    overcurrent devices shall be required to provide overcurrent

    protection in PV source and output circuits. The overcurrent

    devices shall be accessible but shall not be required to

    be readily accessible.

    *690.34 Access to Boxes. *Junction, pull, and outlet boxes

    located behind modules or panels shall be so installed that

    the wiring contained in them can be rendered accessible

    directly or by displacement of a module(s) or panel(s) secured

    by removable fasteners and connected by a flexible

    wiring system.

    This is not a change. Please help me understand the concern.

    Bill Brooks.

    *From:*[email protected]
    <mailto:[email protected]>
    [mailto:[email protected]] *On Behalf Of
    *Ray Walters
    *Sent:* Monday, April 28, 2014 2:23 PM
    *To:* RE-wrenches
    *Subject:* Re: [RE-wrenches] (no subject)

    Interesting so does "require a tool" include taking a screw off
    the cover plate of the combiner box, too?
    What a game changer.  I'm going to Mexico for my next project;
    I'll actually enjoy even more being the sole AHJ on the project.

    R.Ray Walters
    CTO, Solarray, Inc
    Nabcep Certified PV Installer,
    Licensed Master Electrician
    Solar Design Engineer
    303 505-8760  <tel:303%20505-8760>

    On 4/28/2014 2:52 PM, Michael Morningstar wrote:

        Readily accessible is now defined in the 2014 NEC. Installing
        OCPD's underneath a module is a major faux paux, and I can't
        imagine any AHJ thinking otherwise. Having to remove a module
        in order to reset a breaker, what a drag.

        "Capable of being reached quickly for operation, renewal or
        inspection without requiring those concerned to use a tool,
        to climb over, remove obstacle or other."

        Michael



        On Apr 28, 2014, at 10:29 AM, William Miller
        <[email protected] <mailto:[email protected]>> wrote:



            You call it a solar panel, I call it a glass j-box cover
            plate.

            William

            Miller Solar


                On Apr 28, 2014, at 9:21 AM, Jason Szumlanski
                <[email protected] <mailto:[email protected]>>
                wrote:

                If that is the interpretation,
                I don't see how the breakers are "readily accessible"
                in a SolaDeck
                mounted anywhere, regardless of whether it is under a
                module. It
                requires removal of four screws (using a tool) to
                access the breakers
                inside the enclosure. It's all up to the AHJ. It has
                not been an issue
                locally here. I can see how other jurisdictions may not
                concur.



    _______________________________________________
    List sponsored by Home Power magazine

    List Address: [email protected]
    <mailto:[email protected]>

    Change email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
    <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches..org>

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>





_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to