Code insanity. 
There is never voltage on the load side of an open AC switch, arc fault, or 
circuit breaker device supplying a solar inverter that meets UL1741. Solar 
inverters are current sources only, and only while utility voltage is present. 

/wk

William Korthof
714.875.3576
Sustainable Solutions
#956904

On May 27, 2014, at 12:28 PM, Will White <[email protected]> wrote:

We’ve run into the problem in MA where the electrical board suggested we cut 
apart Enphase trunk cable to put it in a raceway.  We all know that isn’t 
possible.
 
From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Bill Brooks
Sent: Tuesday, May 27, 2014 3:18 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] 2014 NEC
 
Nick and Jay,
 
There is a basic problem that products are not currently available to 
specifically address this application. I know Enphase has done a lot of 
research lately about this issue, so they may have uncovered problems that were 
previously not known. My information is that the products are actually 
bi-directional devices. GFCIs are not bi-direction and can fail with voltage on 
the load side of the device. It is possible that some AFCIs have the same 
problem.
 
This AFCI provision is a requirement that was sold to UL and the Code Making 
Panel with the assurance from a very large breaker manufacturer that developing 
products for this application was simple and straightforward.
 
That manufacturer has not stepped forward with a product and so we find 
ourselves in 90.4 land (use the previous version of the code). Some AHJs have 
chosen not to read it that way and have been requiring micro-inverter systems 
to be installed raceways (even though not compatible with raceways). NFPA 
likely have to issue an official interpretation on this since it is unclear 
whether a product will be developed in the reasonable future.
 
Bill.
 
 
 
From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Jay Peltz
Sent: Tuesday, May 27, 2014 11:32 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] 2014 NEC
 
Hi nick
 
Good to know, I was told this by bill brooks at a training a few months ago. 
 
Jay

Sent from my iPhone

On May 27, 2014, at 9:00 AM, Nick Soleil <[email protected]> wrote:

Hi Jay,

It is not acceptable to wire the AFCI breaker with the utility power on the 
output of the AFCI breaker.  That does not meet the specifications for the AFCI 
breakers.  These breakers are sensitive to having voltage on their output when 
the breaker is opened, which can damage the AFCI breakers.

Currently, there are no AFCI circuit breakers that are listed for back-feed.
 

On Tue, May 20, 2014 at 8:10 AM, jay peltz <[email protected]> wrote:
HI Will,
 
You can do this.
 
Take a standard breaker panel, install a Arc fault and run the wiring from the 
enphase like it is the grid: ie into the main lugs.
Then this will go out through the breaker in the correct fashion, and onto the 
main panel.
 
jay
 
peltz power
 
PS as to the code, they want it this way
 
 
On May 20, 2014, at 7:59 AM, Will White wrote:
 
Wrenches,
 
Is anyone else having problems with inspectors and the 2014 NEC?  In Mass we’re 
having all kinds of issues with inspectors requiring/allowing an array of 
different things for 690.12 rapid shut down ranging from roof top disconnects, 
disconnects on the side of a house 20’ up, disconnects in attics, or only 
disconnects that can be activated on the ground.  It varies between inspectors.
 
We’re also having problems with one inspector requiring arc fault breakers on 
Enphase even though there are no UL listed arc fault breakers that can be back 
fed or he wants us to run the trunk cable in a raceway. 
 
It’s getting very difficult to install in Mass.
 
Thanks,
Will
 
Will White
Operations Manager - New England
RGS Energy
64 Main St. |Montpelier, VT 05602
tel 802.223.7804 | mobile 802.234.3167 | fax 802.223.8980
RGSEnergy.com | [email protected]
 
 
 
 
 
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




--
Cordially,
Nick Soleil
Field Applications Engineer
Enphase Energy
Mobile: (707) 321-2937

MyEnlighten is Coming. Get Ready

1420 North McDowell
Petaluma, CA 94954
www.enphase.com
P: (707) 763-4784 x7267
F: (707) 763-0784
E: [email protected]
 
NABCEP Certified Solar PV Installer #03262011-300
California C10 Licensed Electrician #986315
Texas Master Electrician #284451
“Don’t get me wrong: I love nuclear energy! It’s just that I prefer fusion to 
fission. And it just so happens that there’s an enormous fusion reactor safely 
banked a few million miles from us. It delivers more than we could ever use in 
just about 8 minutes. And it’s wireless!” 

- William McDonough

 
This email message is for the sole use of the intended recipient(s) and may 
contain confidential and/or privileged information. If you are not an intended 
recipient, you may not review, use, copy, disclose or distribute this message. 
If you received this message in error, please contact the sender by reply email 
and destroy all copies of the original message. 
 
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 


This email is free from viruses and malware because avast! Antivirus protection 
is active.

 
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to