Hi Kirk

I thought about that, but you'll still need it on for the 5 minute clock. 
If Nick is right and no voltage is acceptable on output side, then I don't see 
how even with relays etc to get it to work?

Jay
Peltz power







> On May 28, 2014, at 7:32 AM, "Kirk Herander" <[email protected]> wrote:
> 
> Sounds like you need the load side of the AFCI to disconnect from the grid if 
> it trips. So you could have a power relay between grid and load side of the 
> AFCI, the relay coil energized from the line side of the AFCI, i.e. the 
> Enphase panel the AFCI is plugged into. So if it trips, power is lost on the 
> Enphase panel buss, and the load side relay opens, disconnecting the AFCI 
> from the grid.
> So no grid power on load side of AFCI when open. Acceptable?
>  
> Kirk Herander
> VT Solar, LLC
> Un-Common PV since 1991
> www.vermontsolarnow.com
> dba Vermont Solar Engineering
> NABCEPTM Inaugural Certificant
> VT RE Incentive Program Partner
> 802.863.1202
>  
> From: RE-wrenches [mailto:[email protected]] On 
> Behalf Of Nick Soleil
> Sent: Tuesday, May 27, 2014 12:01 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] 2014 NEC
>  
> Hi Jay,
> 
> It is not acceptable to wire the AFCI breaker with the utility power on the 
> output of the AFCI breaker.  That does not meet the specifications for the 
> AFCI breakers.  These breakers are sensitive to having voltage on their 
> output when the breaker is opened, which can damage the AFCI breakers.
> 
> Currently, there are no AFCI circuit breakers that are listed for back-feed.
>  
> 
> On Tue, May 20, 2014 at 8:10 AM, jay peltz <[email protected]> wrote:
> HI Will,
>  
> You can do this.
>  
> Take a standard breaker panel, install a Arc fault and run the wiring from 
> the enphase like it is the grid: ie into the main lugs.
> Then this will go out through the breaker in the correct fashion, and onto 
> the main panel.
>  
> jay
>  
> peltz power
>  
> PS as to the code, they want it this way
>  
>  
> On May 20, 2014, at 7:59 AM, Will White wrote:
>  
> Wrenches,
>  
> Is anyone else having problems with inspectors and the 2014 NEC?  In Mass 
> we’re having all kinds of issues with inspectors requiring/allowing an array 
> of different things for 690.12 rapid shut down ranging from roof top 
> disconnects, disconnects on the side of a house 20’ up, disconnects in 
> attics, or only disconnects that can be activated on the ground.  It varies 
> between inspectors.
>  
> We’re also having problems with one inspector requiring arc fault breakers on 
> Enphase even though there are no UL listed arc fault breakers that can be 
> back fed or he wants us to run the trunk cable in a raceway. 
>  
> It’s getting very difficult to install in Mass.
>  
> Thanks,
> Will
>  
> Will White
> Operations Manager - New England
> RGS Energy
> 64 Main St. |Montpelier, VT 05602
> tel 802.223.7804 | mobile 802.234.3167 | fax 802.223.8980
> RGSEnergy.com | [email protected]
>  
>  
>  
>  
>  
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
>  
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
> 
> 
> 
> 
> --
> Cordially,
> Nick Soleil
> Field Applications Engineer
> Enphase Energy
> Mobile: (707) 321-2937
> 
> MyEnlighten is Coming. Get Ready
> 
> 1420 North McDowell
> Petaluma, CA 94954
> www.enphase.com
> P: (707) 763-4784 x7267
> F: (707) 763-0784
> E: [email protected]
>  
> NABCEP Certified Solar PV Installer #03262011-300
> California C10 Licensed Electrician #986315
> Texas Master Electrician #284451
> “Don’t get me wrong: I love nuclear energy! It’s just that I prefer fusion to 
> fission. And it just so happens that there’s an enormous fusion reactor 
> safely banked a few million miles from us. It delivers more than we could 
> ever use in just about 8 minutes. And it’s wireless!” 
> 
> - William McDonough
> 
>  
>  
> This email message is for the sole use of the intended recipient(s) and may 
> contain confidential and/or privileged information. If you are not an 
> intended recipient, you may not review, use, copy, disclose or distribute 
> this message. If you received this message in error, please contact the 
> sender by reply email and destroy all copies of the original message. 
>  
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: [email protected]
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to