To totally protect the AFCI, you'd somehow have to switch the arc-fault breaker 
in circuit after the inverters turn on. You could do it using two breakers in 
the inverter panel, one AFCI, one not, each with a power relay between grid 
panel and load side of the respective breaker. The AFCI relay is off at first, 
the regular breaker relay on. Once the inverters turn on, time delay relays 
energize to the switch AFCI power relay on, wait a second, then switch regular 
breaker power relay off. That way the inverter panel does not lose grid power 
and inverters stay up, and all PV is travelling to the grid panel via the AFCI. 
So for a very short time interval both AFCI and non-AFCI breakers are splitting 
the inverter current to the grid. And of course in this scenario the inverters 
are non-arc fault protected for a very short period of time. At least you'll 
get an inspector scratching their head.

 

My advice: stick with Solaredge. Obviously too much time on my hands today.

 

Kirk Herander

VT Solar, LLC 

Un-Common PV since 1991

www.vermontsolarnow.com

dba Vermont Solar Engineering

NABCEPTM Inaugural Certificant

VT RE Incentive Program Partner

802.863.1202

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Kirk Herander
Sent: Wednesday, May 28, 2014 12:50 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] 2014 NEC AFCI

 

I get it about the delay. If you reset and close the tripped AFCI (or the grid 
comes back up after a power failure), you’ll have to wait 5 mins. before the 
inverters start to push power to the grid. But the AFCI is not being backfed 
during this wait. The same would occur overnight until the inverters wake up in 
the morning. If the AFCI breaker, when closed, is subject to damage with grid 
voltage on the load side when the inverters are not operational, then it’s a 
lot trickier to get the relay scenario to work. Maybe it isn’t doable. 

 

Kirk Herander

VT Solar, LLC 

Un-Common PV since 1991

www.vermontsolarnow.com

dba Vermont Solar Engineering

NABCEPTM Inaugural Certificant

VT RE Incentive Program Partner

802.863.1202

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of jay peltz
Sent: Wednesday, May 28, 2014 11:15 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] 2014 NEC AFCI

 

Hi Kirk

 

I thought about that, but you'll still need it on for the 5 minute clock. 

If Nick is right and no voltage is acceptable on output side, then I don't see 
how even with relays etc to get it to work?

 

Jay

Peltz power

 

 

 

 

 


On May 28, 2014, at 7:32 AM, "Kirk Herander" <[email protected]> wrote:

Sounds like you need the load side of the AFCI to disconnect from the grid if 
it trips. So you could have a power relay between grid and load side of the 
AFCI, the relay coil energized from the line side of the AFCI, i.e. the Enphase 
panel the AFCI is plugged into. So if it trips, power is lost on the Enphase 
panel buss, and the load side relay opens, disconnecting the AFCI from the grid.

So no grid power on load side of AFCI when open. Acceptable?

 

Kirk Herander

VT Solar, LLC 

Un-Common PV since 1991

www.vermontsolarnow.com

dba Vermont Solar Engineering

NABCEPTM Inaugural Certificant

VT RE Incentive Program Partner

802.863.1202

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Nick Soleil
Sent: Tuesday, May 27, 2014 12:01 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] 2014 NEC

 

Hi Jay,

It is not acceptable to wire the AFCI breaker with the utility power on the 
output of the AFCI breaker.  That does not meet the specifications for the AFCI 
breakers.  These breakers are sensitive to having voltage on their output when 
the breaker is opened, which can damage the AFCI breakers.

Currently, there are no AFCI circuit breakers that are listed for back-feed.

 

On Tue, May 20, 2014 at 8:10 AM, jay peltz <[email protected]> wrote:

HI Will,

 

You can do this.

 

Take a standard breaker panel, install a Arc fault and run the wiring from the 
enphase like it is the grid: ie into the main lugs.

Then this will go out through the breaker in the correct fashion, and onto the 
main panel.

 

jay

 

peltz power

 

PS as to the code, they want it this way

 

 

On May 20, 2014, at 7:59 AM, Will White wrote:

 

Wrenches,

 

Is anyone else having problems with inspectors and the 2014 NEC?  In Mass we’re 
having all kinds of issues with inspectors requiring/allowing an array of 
different things for 690.12 rapid shut down ranging from roof top disconnects, 
disconnects on the side of a house 20’ up, disconnects in attics, or only 
disconnects that can be activated on the ground.  It varies between inspectors.

 

We’re also having problems with one inspector requiring arc fault breakers on 
Enphase even though there are no UL listed arc fault breakers that can be back 
fed or he wants us to run the trunk cable in a raceway. 

 

It’s getting very difficult to install in Mass.

 

Thanks,

Will

 


Will White
Operations Manager - New England

RGS Energy

        


64 Main St. |Montpelier, VT 05602
tel 802.223.7804 | mobile 802.234.3167 | fax 802.223.8980


 <http://www.rgsenergy.com/> RGSEnergy.com |  
<mailto:[email protected]> [email protected]

        

 

 

 

 

 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 


_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org






-- 

Cordially,

Nick Soleil

Field Applications Engineer

Enphase Energy

Mobile: (707) 321-2937

 
<http://enphase.com/enlighten_content/myenlighten-launch-site/?utm_source=MyEnlightenPromo&utm_medium=Email_Sig&utm_campaign=MyEnlighten>
 


 
<http://enphase.com/enlighten_content/myenlighten-launch-site/?utm_source=MyEnlightenPromo&utm_medium=Email_Sig&utm_campaign=MyEnlighten>
 MyEnlighten is Coming. Get Ready

 
<http://www.enphase.com/commercial?utm_source=email&utm_medium=sig&utm_campaign=Comm2012>
 


1420 North McDowell

Petaluma, CA 94954

www.enphase.com <http://www.enphaseenergy.com/> 

P: (707) 763-4784 x7267

F: (707) 763-0784

E: [email protected]

 

NABCEP Certified Solar PV Installer #03262011-300

California C10 Licensed Electrician #986315

Texas Master Electrician #284451

“Don’t get me wrong: I love nuclear energy! It’s just that I prefer fusion to 
fission. And it just so happens that there’s an enormous fusion reactor safely 
banked a few million miles from us. It delivers more than we could ever use in 
just about 8 minutes. And it’s wireless!”  

- William McDonough 

 
 
This email message is for the sole use of the intended recipient(s) and may 
contain confidential and/or privileged information. If you are not an intended 
recipient, you may not review, use, copy, disclose or distribute this message. 
If you received this message in error, please contact the sender by reply email 
and destroy all copies of the original message. 
 

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to