Yes Drake, I stand corrected, I was picturing the micro inverters feeding the 
input rather than coupling the output of the Magnum. To your original question, 
I think you would have to be consuming more power than the PV array alone can 
provide before the Magnum voltage would drop with the pump load. So it may be a 
rare event unless the PV array is small. Of course after sundown its all on the 
Magnum. That’s why I suggested two Magnums in my first response.
 
Does anyone know how tolerant the Enphase inverters are of such a momentary sag?

Larry



On Jul 3, 2014, at 1:42 PM, Drake <[email protected]> wrote:

Hi Larry,

In this case, the Enphase will AC couple with the Magnum in the protected loads 
panel. The AC out of the Magnum provides the micro grid to which the Enphase 
connects. If  charging exceeds loads, when the grid is down, power will go to 
the batteries (up to the high battery voltage set point). If loads are greater 
than the output of the Enphase system, the Magnum will produce power to feed 
the loads.

Thanks,

Drake

At 10:55 AM 7/3/2014, you wrote:
> Hi Drake,
> 
> If the Enphase are online, up to 60 amps (30A @ 240V) can be transferred 
> through the Magnum inverter to loads. The inverter is not providing power to 
> loads at that time. If the Enphase go offline, the Magnum takes over using 
> power from the battery. If the load is greater than your Enphase system can 
> provide, the Magnum will transfer to battery power based on the VAC dropout 
> setting. You probably want to use the UPS mode (read ME-ARC manual about 
> this).
> 
> The new Magnum MSH models can combine AC input power and battery power to 
> increase the total AC output capacity for starting heavy loads.
> 
> Larry
> 
> 
> 
> On Jul 3, 2014, at 7:59 AM, Drake <[email protected]> 
> wrote:
> 
> This information helps greatly. I really appreciate all of your expert advice.
> 
> One other wild card in the installation is that the inverter is going to be 
> AC coupled with an Enphase system. The Enphase system will contribute greatly 
> to the overall power available in the protected loads panel. But, with 
> Magnum's slow voltage response I'm not sure if the Enphase system will drop 
> off line when the pump surges, or if the Enphase power will be available to 
> help with the startup surge.
> 
> Any insights on this?
> 
> Thank you,
> 
> Drake
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to