What has been everybody’s experience with Full River Batteries?

 

Bob

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Roy Butler
Sent: Wednesday, July 02, 2014 3:12 PM
To: [email protected]
Subject: Re: [RE-wrenches] Magnum and Pumps

 

Sweet....thanks for that info, I stand corrected!



Roy Butler
NABCEP Certified Solar PV Installer®
NYSERDA eligible PV & wind installer
IREC Certified Master Trainer™ for Small Wind Installer
Four Winds Renewable Energy, LLC
8902 Route 46, Arkport, NY 14807
607-324-9747  www.four-winds-energy.com
 
Join us at the 10th Annual Small Wind Conference
A Gathering of Installers, Manufacturers, Dealers, & Distributors
June 17 and 18, 2014 in Stevens Point, Wisconsin
www.smallwindconference.com
 
Although no trees were killed in the sending of this message, 
a large number of electrons were terribly inconvenienced.
 
                

On 7/2/2014 2:55 PM, Larry Crutcher, Starlight Solar Power Systems wrote:

Hi Roy, 

 

The FullRiver DC400-6 AGM battery can issue 2000 amps for 5 seconds so he 
should be fine.

 

Larry

On Jul 2, 2014, at 12:35 PM, Roy Butler <[email protected]> wrote:

 

I haven't seen anyone mention the battery bank. If I understand correctly, 
there's a single string of sealed
L16 batteries on this inverter. I have my doubts as to whether or not that bank 
can provide the high current
the inverter needs to start this load.



Roy Butler
NABCEP Certified Solar PV Installer®
NYSERDA eligible PV & wind installer
IREC Certified Master Trainer™ for Small Wind Installer
Four Winds Renewable Energy, LLC
8902 Route 46, Arkport, NY 14807
607-324-9747  www.four-winds-energy.com <http://www.four-winds-energy.com/> 
 
Join us at the 10th Annual Small Wind Conference
A Gathering of Installers, Manufacturers, Dealers, & Distributors
June 17 and 18, 2014 in Stevens Point, Wisconsin
www.smallwindconference.com <http://www.smallwindconference.com/> 
 
Although no trees were killed in the sending of this message, 
a large number of electrons were terribly inconvenienced.
 
                

On 7/2/2014 2:10 PM, Jason Szumlanski wrote:

To further qualify my statements, the inverter will start the pump without 
issue, but I should echo the warnings by others that if there are other loads 
present, especially other motor loads that could start ​concurrently, you may 
experience issues. As long as your customer understands the limitations and 
possibilities, you may be just fine.

 

Jason Szumlanski

​ Fafco Solar​

 

  
<http://ws-stats.appspot.com/ga/pixel.png?yes__count=true%20&e=legacy_impression>
 

 

On Wed, Jul 2, 2014 at 11:00 AM, Jason Szumlanski <[email protected]> wrote:

For what it's worth, I've run a single speed 1.5HP pool pump with a MS4448PAE 
in a mobile application on a 38.4kWh battery bank (sixteen Rolls S-530's). I 
have also run a 2.5HP Hayward EcoStar Variable Speed pool pump at full RPM, but 
that startup current is likely less than you well pump.

 

I'm going to guess your 3/4HP well pump will be a breeze to start with this 
inverter.

 

Jason Szumlanski 

​ Fafco Solar​

 

 

On Wed, Jul 2, 2014 at 10:47 AM, Allan Sindelar <[email protected]> wrote:

Drake,
As a normal CYA, I'll always gently let a customer know that this (or any) 
particular combination of inverter and load sometimes proves incompatible, just 
in case the unexpected happens. (We once had a MS4448 that would not reliably 
start and run a condensing boiler; a switch to a different boiler resolved the 
issue.)

Having said that note of caution, I wouldn't give it any concern. 3/4 HP and 1 
HP well pumps have never been an issue; I would expect 1.5 HP to be easy to 
run. At 2 HP I'd be asking these questions here. 

You might check that it's a 3-wire, capacitor-start motor, but nowadays nearly 
all are. Two-wire pumps (with no control box) can add 50% to the surge.

The Magnum has a fairly poor voltage regulation response. Sometimes the AC 
voltage can drop to ~80 VAC momentarily. So you might also caution your 
customer that the lights may flicker when the pump starts. In our home we know 
whenever our Kenmore fridge turns on.

Allan

Allan Sindelar
[email protected]
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
505 780-2738 <tel:505%20780-2738>  cell

 

On 7/2/2014 8:17 AM, Drake wrote:

Hello Wrenches,

We are hoping to use a Magnum PAE 4448 to back up a household that includes a 
3/4 HP deep well pump. There is about 120 feet of vertical rise and about 1000 
feet of horizontal distance. 

I have been told that there is a correlation between the locked rotor current 
of a pump and the predictable ability of a specified inverter to power that 
pump. 

The plumber who installed the pump left no paperwork and retained no records of 
what pump he put in the hole last year. He could only say it was a 3/4 HP pump. 
We are therefore unable to obtain the manufacturer's nameplate specifications.

The Magnum PAE 4448 has a 1 mS surge of 70 A (at 240 V) and a 100 MS surge of 
40 A. According to the NEC Table 430.251(A), a 3/4 HP motor has a locked rotor 
current of 41.4 amps at 230 V. 

This inverter can surge at 35.4 A for 5 seconds. The specified battery bank 
will be 8 Full River  L-16 AGMs. Can anyone say if: 

*       Is there enough information to know if this setup will handle the pump, 
and if so, will it? 
*       How can an inverter's ability to power a motor or pump be calculated by 
knowing its locked rotor current? Which surge periods should be compared to the 
locked rotor current? 
*       Does the surge current need to equal locked rotor. How long must the 
inverter meet its required maximum surge? 
*       From experience with Magnums and pumps, does this seem like a good 
combination? 


Thank you,

Drake 

Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV 
740-448-7328
http://athens-electric.com/ 






_______________________________________________
List sponsored by Redwood Alliance
 
List Address: [email protected]
 
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/> 
 

 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

 






_______________________________________________
List sponsored by Redwood Alliance
 
List Address: [email protected]
 
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out or update participant bios:
www.members.re-wrenches.org
 

 

  _____  

No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4592 / Virus Database: 3986/7776 - Release Date: 07/01/14

  _____  

No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4592 / Virus Database: 3986/7776 - Release Date: 07/01/14

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to