does your customer have any issues or is this a first inspection type call
just to see
Jerry


On Tue, Aug 12, 2014 at 3:54 PM, Mac Lewis <[email protected]> wrote:

> Hello wrenches,
>
> I just went on a service call for a new client.  He had a bank of 4 year
> old Interstate L16HCL batteries, 2 strings of 8, 48V system, 840Ahr.  We
> went through the batteries and got specific gravity on all of the cells
> post-equalization.  I was a bit surprised to see some very high numbers ie
> over 1.32 for the specific gravities (higher than my refractometer goes).
>  The specific gravities were all over the place, but I haven't seen numbers
> this high.  I don't have a great explanation.  He has a stacked 3648 VFX
> Outback system, and the set-points were 58.8V Absorb for 2 hours, and 62V
> Equalize for 2 hours.  He has a decent amount of solar (about 3400W) and a
> 1000W wind generator.
>
> Any ideas why the specific gravity is so high on some cells?  Also, is
> there anything wrong with having SG this high, post-equalization?  For this
> very standard battery, what settings do you go with (Bulk, Absorb, Float,
> Eq, and times for Abs and Equalization).
>
> Thanks in advance
>
>
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates *
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to