Friends:

 

I met with the AV crew yesterday.  They are completely unwilling to run the 
system without a UPS.  I have some choices:

 

1.    See if we have a real problem, and if so, how bad is it?

2.    Temporarily disable the Sunny Boy inverters to see if eliminating the 
Frequency Shift Power Control (FSPC) makes the UPS happier.  I have done this 
and am waiting for results.

3.    If the above creates good results, consider removing the Sunny Boy 
inverters and rely on direct DC battery charging, maybe by using Morningstar 
MPPT-600 charge controllers.

4.    Find out if the inverters, generator or both are causing a problem.

5.    If it is the generator, have it repaired or try to reprogram the Sunny 
Island inverters to disable transfer and utilize battery charging only.  Has 
anyone done this?

6.    If it is the inverters, have them repaired or select another product.

7.    If I am confident that power quality is adequate, mute the UPS and ignore 
it.

 

I will let you know how this progresses because I think there is interest and 
others have experienced similar problems.

 

William

 

 

Gradient Cap_mini
Lic 773985
 <http://www.millersolar.com/> millersolar.com
805-438-5600

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Steve Jefferson
Sent: Friday, August 15, 2014 11:11 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] More Sunny Island power problems

 

Afternoon William,

 

The communication is there to send the signal to the Sunny Boys to go into 
off-grid mode, when the grid fails. 

Frequency shift still occurs when current is not needed from the SBoy’s. 

 

I typically would not recommend that a UPS circuit be placed in the protected 
loads panel.

The UPS is looking for grid issues, and I think the frequency shift feature 
would probably fall under that.

 

As for the SI frying the UPS, it is my opinion that the UPS failed. It should 
have disconnected and started to provide backup power to its loads when the SI 
started to shift the freq.

That’s its job.

 

I Still think it is a good idea to examine the SI data, maybe you can figure 
out if the SI was in Freq shift mode when the UPS failed.

 

Thanks 

 

SMA America, LLC

Steve Jefferson

Service Line Supervisor

3925 Atherton Ave

Rocklin, CA 95765 - 3714

U.S.A.

Tel:  +1 916 625 3185 (direct)

Fax: +1 916 625 0871

Mobile: +1 916 622 4253

Email: [email protected]

 <http://www.sma-america.com/> www.SMA-America.com

 

 <http://www.youtube.com/watch?v=yQWzPuyqhzo&feature=youtu.be> 
cid:[email protected]

 

This email and any attachments thereto may contain SMA America, LLC 
confidential, privileged and private material for the sole use of the intended 
recipient. Any review, copying, or distribution of this email (or any 
attachments thereto) by others is strictly prohibited. If you are not the 
intended recipient, please contact the sender immediately and permanently 
delete the original and any copies of this email and any attachments thereto. 
Thank you.

 

 

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of William Miller
Sent: Friday, August 15, 2014 9:55 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] More Sunny Island power problems

 

Mac:

 

I will review the data.  Thanks!

 

William

 

Gradient Cap_mini
Lic 773985
millersolar.com <http://www.millersolar.com/> 
805-438-5600

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Mac Lewis
Sent: Friday, August 15, 2014 9:46 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] More Sunny Island power problems

 

William, 
As far as I understand, the communication is supposed to take away the need for 
frequency shift. Have you pulled the data off of the Sim card and looked for 
frequency shift?

On Aug 15, 2014 10:24 AM, "William Miller" <[email protected]> wrote:

Friends:

 

A Sunny Island mini-grid system I am maintaining also does not play nice with a 
UPS unit.  So much so that the system reportedly fried a Furman UPS unit 
yesterday!  

 

This should not be!  The UPS unit is supposed to protect downstream equipment 
and should be able to protect itself as well.  

 

I need to rent some high quality power monitoring equipment to monitor voltage, 
frequency and distortion.  I need one three phase unit in the power building 
and I need something more compact for the AV equipment room.  Does anyone have 
a recommendation for models that might work in this scenario?

 

The thought occurred to me that the system by which the Sunny Island varies 
line frequency may be problematic for sensitive electronics.  I have connected 
the Sunny Island master to the Sunny Boys with RS485 and programmed the Sunny 
Boys for off-grid.  Can this allow the two systems to communicate to regulate 
PV charge without relying on frequency shifting?

 

Thanks in advance.

 

William

 

 

Gradient Cap_mini
Lic 773985
millersolar.com <http://www.millersolar.com/> 
805-438-5600

 


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to