William,
One other option, if the AV crew can see the light, is replace the UPS with an 
inverter like Magnum MS1012 and a separate battery equal to the UPS capacity. 
The Magnum has broad input voltage and should the SB fail to provide power, the 
transfer time is likely fast enough (16ms) to replicate the UPS. Use a high Vac 
dropout setting in this case.

Just trying to think outside the box. I’ve done this in RV’s and it works fine.

Larry

On Aug 16, 2014, at 1:03 PM, William Miller <[email protected]> wrote:

Friends:
 
I met with the AV crew yesterday.  They are completely unwilling to run the 
system without a UPS.  I have some choices:
 
1.    See if we have a real problem, and if so, how bad is it?
2.    Temporarily disable the Sunny Boy inverters to see if eliminating the 
Frequency Shift Power Control (FSPC) makes the UPS happier.  I have done this 
and am waiting for results.
3.    If the above creates good results, consider removing the Sunny Boy 
inverters and rely on direct DC battery charging, maybe by using Morningstar 
MPPT-600 charge controllers.
4.    Find out if the inverters, generator or both are causing a problem.
5.    If it is the generator, have it repaired or try to reprogram the Sunny 
Island inverters to disable transfer and utilize battery charging only.  Has 
anyone done this?
6.    If it is the inverters, have them repaired or select another product.
7.    If I am confident that power quality is adequate, mute the UPS and ignore 
it.
 
I will let you know how this progresses because I think there is interest and 
others have experienced similar problems.
 
William
 
 
<image001.jpg>
Lic 773985
millersolar.com
805-438-5600
 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to