Truth is there is likely more than enough capacity in the LFP battery the 
customer has but the manufacturer built a limit into the “box". The limit of 
our battery is set to 10C for 30 seconds. WAY more than any inverter can draw 
with even a small bank.

Larry

On Sep 18, 2014, at 12:26 PM, [email protected] wrote:


Yes, well of course there are these details.
  If the LFP surge is a limitation, but not its amount of overall
energy storage, then you may have to add a very large amount of LFP storage to 
overcome that which
could be overkill and cost a lot of extra $.

It's all a compromise.

boB


On 9/18/2014 10:55 AM, Starlight Solar Power Systems wrote:
> boB,
> 
> When charging a LFP battery, the  charge terminates when absorb voltage is 
> reached unless you have an enormous charger in which case you will need to 
> terminate based on AH returned. You would also need to isolate the LA battery 
> to finish charging it. Plus, LA needs higher voltages than LFP. I don’t think 
> would solve Williams problem. A better solution would be another LI-ion bank 
> that is not current limited. Just a 50AH bank could provide an additional 
> 500amps.
> 
> Larry
> 
> On Sep 18, 2014, at 11:09 AM, [email protected] wrote:
> 
> 
> One thing that could possibly be done is to have a smaller lead acid battery 
> in parallel with the LiFePo bank
> so the LiFePo contains most of the "energy" storage, but the LA can supply 
> the surges and low impedance
> source voltage.
> 
> boB
> 
> 
> 
> On 9/18/2014 8:53 AM, Starlight Solar Power Systems wrote:
>> William,
>> 
>> This is one reason I choose to avoid the "black box" approach to Li-ion 
>> batteries for our customers. There are several companies offering enclosed 
>> battery/controls like the OES. Their approach does not match well to the 
>> off-grid and mobile markets that I serve. 
>> 
>> Since most LFP batteries can handle 10C for up to 30 seconds (Winston LFP 
>> can surge to 20C!) and 2C-3C continuous discharge, it makes sense to me to 
>> design a protection system that can't utilize that capability. Our LFMP 
>> battery has an external CPU that I can program. We also use external high 
>> current relays for the protective circuits so the full load of the inverter 
>> can be put to use.
>> 
>> With a LFP battery bank of 48 volts and 400AH, somewhat small for off grid, 
>> the battery can operate continuously at 1200 amps or about 60kW output and 
>> surge to 4000 amps/600kW. This obviously is way beyond the demand capability 
>> of the inverter(s). A quick look at the SI6048 data sheet shows maximum AC 
>> current is 11kW for 3 seconds.
>> 
>> I am glad you noticed the extremely low voltage sag under load. This feature 
>> means lower current which should translate to longer life for inverters. It 
>> also means starting loads that you can’t with a similar sized lead acid 
>> battery. A 1C load typically has only 0.2 volt sag. For 48 volt systems, 
>> this means maintaining 51.2 volts throughout the full battery use. In fact, 
>> a 1C load will still only have 0.2 volt drop until about 90% discharged. 
>> Simply amazing.
>> 
>> Larry Crutcher
>> 
>> 
>> On Sep 17, 2014, at 10:15 PM, William Miller <[email protected]> wrote:
>> 
>> Larry:
>>  
>> …...The internal battery management system will allow them to disconnect 
>> under surge loads, just when you need your batteries to stay connected.  I 
>> will be conversing with the manufacturer to learn more about them.
>>  
>> William
>>  
>> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to