Eaton has a line of disconnects that may fit the bill:

 

http://www.eaton.com/Eaton/ProductsServices/Electrical/ProductsandServices/ElectricalDistribution/SwitchesandDisconnects/SolarDisconnects/index.htm#tabs-2

 

Ryan

 

 

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of August Goers
Sent: Tuesday, October 07, 2014 11:30 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] TL inverter with long DC Feeder

 

William,

 

I see now from the separate post from Michael Kelly of Solectria that indeed 
you cannot combine your two strings with this inverter. I think that leaves you 
stuck with four separate disconnect switches unless someone on this list knows 
of a four pole DC rated disconnect switch. Or, you’ll have to switch inverters. 
I have never installed these Solectria inverters so I don’t know much about 
them. 

 

Best,

 

August

Luminalt

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of William Miller
Sent: Tuesday, October 07, 2014 8:28 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] TL inverter with long DC Feeder

 

August:

 

I have been told I can't combine upstream of the inverter. 

 

William


Miller Solar


On Oct 7, 2014, at 8:03 AM, August Goers <[email protected]> wrote:

William,

 

We have bumped into similar dilemmas when needing remote DC disconnects with TL 
inverters. I believe the Solectria you are using has two MPPTs? Ideally, you 
would keep each string separate to benefit from the dual trackers – this would 
mean four DC disconnects if you went with a standard product like a Square D 
HU361RB. If you combine each of the two strings out at the array(s) then you 
could get away with two disconnects, one for each inverter. Neither option is 
ideal.

 

Best,

 

August

 

Luminalt

 

 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to