William,

        Just about a week ago I asked Greg Smith at SMA to confirm that it 
would be appropriate to use THWN-2 in the buried PVC conduit for the DC run 
from a pole mount array with it's DC disco to the SMA DC disco below their 
inverter......Just to be sure you're not thinking you have to use PV wire all 
the way back to the DC disco at the inverter.  He confirmed that THWN-2 used 
for the run from the array disco was AOK.

        We have been using Midnight discos with touch-safe fuses and clear 
signage to not disconnect under load.....authorized solar bozos only.

Bill


  ----- Original Message ----- 
  From: William Miller 
  To: RE-wrenches 
  Sent: Monday, October 06, 2014 11:40 AM
  Subject: [RE-wrenches] TL inverter with long DC Feeder


  Wrenches:

   

  We are getting up to speed on using transformer-less inverters.  I have 
advocated long for the additional safety offered by these inverters but I am 
realizing the trade-offs with the new technology:  The implementation gets more 
complicated with the requirement for PV wire, OCPD and disconnecting means for 
plus and minus and plus providing  Arc Flash rated equipment.

   

  I am currently designing a system that will locate the PV about 400 feet from 
the residence.  The system will utilize 2 Solectria 5200 watt inverters at the 
residence.  I would like to provide disconnecting means for the 4 strings at 
the array, in case of any needed service or excavating.  Preferably I'd like 
the disconnecting means to be deployable by a lay person (i.e. the gardener).

   

  Finding an 8 pole, arc flash, 600 VDC rated disconnect is not easy.  I could 
install an Outback 8 circuit combiner with 8 touch-safe fuse holders.  The new 
combiners have had dead-fronts for a while now.  The gardener needs only to 
have a Philips screw driver to open this cover.  Any better ideas out there?

   

  Thanks,

   

  William

   

   


  Lic 773985
  millersolar.com
  805-438-5600

   



------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Redwood Alliance

  List Address: [email protected]

  Change listserver email address & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out or update participant bios:
  www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to