Sorry William. My mixup/mistake.
The switch is only 4 poles, not 8 poles.
I meant 8 fuses for 4 PV strings for non-isolated/ungrounded PV systems
and 2 separate outputs for dual MPPT input inverters.
boB
On 10/9/2014 11:46 AM, William Miller wrote:
Bob:
I reviewed the link you sent and I do not see any reference to an 8
pole disconnect. Could you clarify, please?
Thanks,
William Miller
Gradient Cap_mini
Lic 773985
millersolar.com <http://www.millersolar.com/>
805-438-5600
*From:*RE-wrenches [mailto:[email protected]]
*On Behalf Of *[email protected]
*Sent:* Wednesday, October 08, 2014 11:46 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] TL inverter with long DC Feeder
William,
There is this DLTL disco with 8 poles. I understand that the "street
price" is very possible less than the $579 4-pole you cited earlier.
For future reference, this is also rapid shutdown ready.
http://www.midnitesolar.com/productPhoto.php?product_ID=583&productCatName=RAPID-SHUTDOWN-SYSTEM-NEC-690.12&productCat_ID=44&sortOrder=2&act=p
boB
On 10/7/2014 7:52 PM, William Miller wrote:
Jeremy:
With 4 strings of PV into 2 transformerless inverters, I would
need 2 of them. At $579.00 each this is a deal killer.
William
Gradient Cap_mini
Lic 773985
millersolar.com <http://www.millersolar.com/>
805-438-5600
*From:*RE-wrenches
[mailto:[email protected]] *On Behalf Of
*All Solar, Inc.
*Sent:* Tuesday, October 07, 2014 4:28 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] TL inverter with long DC Feeder
Use the Midnite SOB series.
They have a 4 pole
Jeremy Rodriguez,
President
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org