Hi ray. ,
There is the diversion "solid state" for SS  relays. 

Jay
Peltz power




> On Dec 5, 2014, at 3:08 PM, Ray Walters <[email protected]> wrote:
> 
> I don't believe the aux is PWM.  It should be a straight 12 v 200 mA output 
> as I recall.  Its just enough to run a battery fan, or a 12 v relay.  You 
> shouldn't need anything else.  Being current limited, it doesn't even need a 
> fuse.
> Also you need to run both leads (pos and neg) from the aux output to the 
> control side of the relay.  It is its own output and you will probably cause 
> unfortunate things to happen if wired in common with anything else.  I 
> usually use signal wire with multiple conductors, so trying to get away from 
> one control conductor is fool hardy anyway.
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer, 
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
> On 12/5/2014 3:09 PM, Hugh Piggott wrote:
>> Hi Hugh again
>> Just to clarify the set up:
>> The SSR controls the AC power from the inverter to the heating load.  It 
>> switches partway through each half cycle and thus controls the power to the 
>> load.
>> The input to the SSR requires a power supply 8-32 V present all the time it 
>> is working.  I suppose it might be feasible to take this from  the AUX but 
>> as this will be pulsing PWM I don't want to rely on that.  Its a supply 
>> voltage to the input and not a control signal and for that reason I want to 
>> take it from the main battery which happens to be a 24 volt one which is 
>> ideal.
>> The control signal is 0-10 volts DC and this controls the amount of power 
>> the unit delivers smoothly.  I want to get this from a capacitor that 
>> charges off the aux output so that is turns the PWM into an analog voltage 
>> signal that controls the SSR and controls the load.  I do this all the time 
>> with tristar outputs so it does work.  I have just never done it with the 
>> AUX of a FM80 controller.
>> 
>> So my question again is simply this.  Can I connect the ground of the AUX to 
>> the inverter batter ground negative?  Most likely it is already connected, 
>> but I'd like to know if connecting it will damage the FM80.  I am also 
>> trying the outback forum.
>> 
>> thanks for any help
>> Hugh
>> 
>>> On 5 Dec 2014, at 18:44, Hugh Piggott wrote:
>>> 
>>> hi wrenches,
>>> 
>>> I am installing some load controls for a client who has a FM80 controller. 
>>> I don't have experience with this product. It has a 12V aux output that I 
>>> wish to drive an SSR but the wiring is complicated by the fact that this 
>>> SSR also needs a power supply as well as a control signal. I want to use 
>>> 24V nominal system battery for the SSR power and AUX for the signal. Can I 
>>> connect the grounds together?
>>> 
>>> Additional info. I am using a phase control SSR driven by a 0-10 volt 
>>> signal to control an AC load with phase angle shift control. I plan to put 
>>> an RC filter that converts the PWM output of the AUX from the CC to give an 
>>> analog voltage output that determines the loading of the inverter. Crydom 
>>> MCPC2450
>>> 
>>> thanks for any help before I go on site next week
>>> Hugh
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: [email protected]
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://www.mail-archive.com/[email protected]/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/[email protected]/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to