I use 3-32vdc SS relays all the time powered from the AUX relay ( xantex, 
classic,outback). 
They work just fine in fast and slow PWM 
And switching both AC or DC, with correct relay of course. 

As to connecting the ground, that I can't tell you. But your ohm meter should 
tell you no?

Jay
Peltz power






> On Dec 5, 2014, at 2:09 PM, Hugh Piggott <[email protected]> wrote:
> 
> Hi Hugh again
> Just to clarify the set up:
> The SSR controls the AC power from the inverter to the heating load.  It 
> switches partway through each half cycle and thus controls the power to the 
> load.
> The input to the SSR requires a power supply 8-32 V present all the time it 
> is working.  I suppose it might be feasible to take this from  the AUX but as 
> this will be pulsing PWM I don't want to rely on that.  Its a supply voltage 
> to the input and not a control signal and for that reason I want to take it 
> from the main battery which happens to be a 24 volt one which is ideal.
> The control signal is 0-10 volts DC and this controls the amount of power the 
> unit delivers smoothly.  I want to get this from a capacitor that charges off 
> the aux output so that is turns the PWM into an analog voltage signal that 
> controls the SSR and controls the load.  I do this all the time with tristar 
> outputs so it does work.  I have just never done it with the AUX of a FM80 
> controller.
> 
> So my question again is simply this.  Can I connect the ground of the AUX to 
> the inverter batter ground negative?  Most likely it is already connected, 
> but I'd like to know if connecting it will damage the FM80.  I am also trying 
> the outback forum.
> 
> thanks for any help
> Hugh
> 
>> On 5 Dec 2014, at 18:44, Hugh Piggott wrote:
>> 
>> hi wrenches,
>> 
>> I am installing some load controls for a client who has a FM80 controller. I 
>> don't have experience with this product. It has a 12V aux output that I wish 
>> to drive an SSR but the wiring is complicated by the fact that this SSR also 
>> needs a power supply as well as a control signal. I want to use 24V nominal 
>> system battery for the SSR power and AUX for the signal. Can I connect the 
>> grounds together?
>> 
>> Additional info. I am using a phase control SSR driven by a 0-10 volt signal 
>> to control an AC load with phase angle shift control. I plan to put an RC 
>> filter that converts the PWM output of the AUX from the CC to give an analog 
>> voltage output that determines the loading of the inverter. Crydom MCPC2450
>> 
>> thanks for any help before I go on site next week
>> Hugh
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/[email protected]/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to