Hi Mac,
Jay just had the same issue and it was 120v from the gen instead of 120/240. 
The inverter was charging using half the windings causing it to Overtemp.

Check the 60A breakers on the side of the inverter. Also make sure to remove 
the wires from the input terminal block before measuring voltage as the 
inverter will make 120v look like 120/240v at the terminals.

If the generator is 3 Phase it won't work with this inverter unless you only 
use one leg. This will work but you will need to turn the charge rate to 50% in 
order to prevent Overtemp. Sometimes it works as high as 70%.

Gary Baxter
Product Manager
Magnum/Dimensions

On Dec 15, 2014, at 12:12 PM, Mac Lewis 
<[email protected]<mailto:[email protected]>> wrote:


Hi jarmo,

We have verified this is split phase 120/240. My multimeter gets 120 L-N and 
240 L-L.

Thanks

On Dec 15, 2014 10:25 AM, 
<[email protected]<mailto:[email protected]>>
 wrote:
Hi:

The Generac QT02224GNAX ships as a three-phase 120/208 VAC.  I believe the 
Magnum is a 120/240 VAC.

JARMO
_____________________________________________________________________________________

Jarmo Venalainen  |   Schneider Electric   |  Solar Business  |   CANADA  |   
Training & Development Specialist - Senior
Phone: +604-422-2528<tel:%2B604-422-2528>  |   Fax: 
+604-420-1591<tel:%2B604-420-1591>  |   Mobile: 
+604-505-0291<tel:%2B604-505-0291>
Email: 
[email protected]<mailto:[email protected]>
  |   Site: www.SEsolar.com<http://www.sesolar.com/>  |   Address: 3700 Gilmore 
Way, Burnaby, BC V5G4M1

<mime-attachment.jpg><http://%20www.sesolar.com/>
*** Please consider the environment before printing this e-mail



From:   Mac Lewis <[email protected]<mailto:[email protected]>>
To:     RE-wrenches 
<[email protected]<mailto:[email protected]>>,
Date:   12/15/2014 05:52 AM
Subject:        [RE-wrenches] Generac QT series
Sent by:        "RE-wrenches" 
<[email protected]<mailto:[email protected]>>

________________________________



Hello wrenches,

We have a newly installed system that has a 22 kW Generac Quiet Source 
QT02224GNAX with a Magnum MS4448-PAE.  When we start the generator, the 
Magnum's internal transformer temperature climbs to overtemp (240F) within a 2 
minutes.  The batteries are being floated at the time, and haven't seen more 
than 5A coming out of the generator.  We swapped the Magnum out, and we have 
the exact same issue.  We then got a job-site gas generator 6500W and ran it.  
No problem whatsoever.  The problem appears to be with the Generac, or with the 
interaction between the Generac & the Magnum.  I didn't have a scope on site 
but the fluke multimeter doesn't detect anything wrong with the voltage or 
frequency coming from the Generac.

Has anyone had issues with the Generac QT?  Anyone paired one with a Magnum PAE 
before?  I want to get my scope up there and look for triplen harmonics, but 
I'm not sure how to filter these out.  Any references on how to effectively do 
that is appreciated.

Thanks in advance

--



Mac Lewis

"Yo solo s? que no s? nada." -S?crates

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
_____________________________________________________________________________________________________________________
List sponsored by Redwood Alliance

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>


_______________________________________________
List sponsored by Redwood Alliance

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>


_______________________________________________
List sponsored by Redwood Alliance

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to