If memory serves me correctly and this is the off grid Generac they are 
available as a 120 volt and it takes a new breaker and rewiring to get 120 / 
240 out of them

I run into this in the past they actually had it wired for 240 into a balancing 
transformer to feed 120 into the inverter

We could've just left it at 120 volt 

Later,
Bob ellison 


Bob Ellison

> On Dec 16, 2014, at 11:33 AM, "Baxter, Gary" <[email protected]> wrote:
> 
> Hi Mac,
> Jay just had the same issue and it was 120v from the gen instead of 120/240. 
> The inverter was charging using half the windings causing it to Overtemp.
> 
> Check the 60A breakers on the side of the inverter. Also make sure to remove 
> the wires from the input terminal block before measuring voltage as the 
> inverter will make 120v look like 120/240v at the terminals.
> 
> If the generator is 3 Phase it won't work with this inverter unless you only 
> use one leg. This will work but you will need to turn the charge rate to 50% 
> in order to prevent Overtemp. Sometimes it works as high as 70%.
> 
> Gary Baxter
> Product Manager
> Magnum/Dimensions
> 
> On Dec 15, 2014, at 12:12 PM, Mac Lewis <[email protected]> wrote:
> 
>> Hi jarmo,
>> 
>> We have verified this is split phase 120/240. My multimeter gets 120 L-N and 
>> 240 L-L.
>> 
>> Thanks
>> 
>>> On Dec 15, 2014 10:25 AM, <[email protected]> wrote:
>>> Hi: 
>>> 
>>> The Generac QT02224GNAX ships as a three-phase 120/208 VAC.  I believe the 
>>> Magnum is a 120/240 VAC. 
>>> 
>>> JARMO
>>> _____________________________________________________________________________________
>>>  
>>> 
>>> Jarmo Venalainen  |   Schneider Electric   |  Solar Business  |   CANADA  | 
>>>   Training & Development Specialist - Senior 
>>> Phone: +604-422-2528  |   Fax: +604-420-1591  |   Mobile: +604-505-0291 
>>> Email: [email protected]  |   Site: www.SEsolar.com  
>>> |   Address: 3700 Gilmore Way, Burnaby, BC V5G4M1 
>>> 
>>> <mime-attachment.jpg>
>>> *** Please consider the environment before printing this e-mail 
>>> 
>>> 
>>> 
>>> From:       Mac Lewis <[email protected]>
>>> To: RE-wrenches <[email protected]>,
>>> Date:       12/15/2014 05:52 AM
>>> Subject:    [RE-wrenches] Generac QT series
>>> Sent by:    "RE-wrenches" <[email protected]>
>>> 
>>> 
>>> 
>>> Hello wrenches, 
>>> 
>>> We have a newly installed system that has a 22 kW Generac Quiet Source 
>>> QT02224GNAX with a Magnum MS4448-PAE.  When we start the generator, the 
>>> Magnum's internal transformer temperature climbs to overtemp (240F) within 
>>> a 2 minutes.  The batteries are being floated at the time, and haven't seen 
>>> more than 5A coming out of the generator.  We swapped the Magnum out, and 
>>> we have the exact same issue.  We then got a job-site gas generator 6500W 
>>> and ran it.  No problem whatsoever.  The problem appears to be with the 
>>> Generac, or with the interaction between the Generac & the Magnum.  I 
>>> didn't have a scope on site but the fluke multimeter doesn't detect 
>>> anything wrong with the voltage or frequency coming from the Generac. 
>>> 
>>> Has anyone had issues with the Generac QT?  Anyone paired one with a Magnum 
>>> PAE before?  I want to get my scope up there and look for triplen 
>>> harmonics, but I'm not sure how to filter these out.  Any references on how 
>>> to effectively do that is appreciated. 
>>> 
>>> Thanks in advance 
>>> 
>>> -- 
>>> 
>>> 
>>> 
>>> Mac Lewis
>>> "Yo solo sé que no sé nada." -Sócrates
>>> 
>>> 
>>> ______________________________________________________________________
>>> This email has been scanned by the Symantec Email Security.cloud service.
>>> _____________________________________________________________________________________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: [email protected]
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://www.mail-archive.com/[email protected]/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> 
>>> 
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: [email protected]
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://www.mail-archive.com/[email protected]/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/[email protected]/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to