The inverters' input capacitors may be charged and so that must also be isolated near the inverter.

A grid operated contactor will not work for a battery-back up system.

Also, 600V DC can weld contacts closed and if this happens and there is no feedback to show that
the contacts definitely opened, this can ruin a firefighter's day.

Otherwise, a system of contactors from AC grid could work in a grid-tie only system.

The new UL rapid shutdown specifications are supposed to be released very soon now.
Maybe within the month ?

boB Gudgel
K7IQ
MidNite Solar


On 2/2/2015 1:23 PM, Mark Frye wrote:
In order to clear up the conversation...

I you put a relay in a box within 10 feet of the array on the roof, you can use an relay with a DC rated Normally Open contact to open and connect/isolate the array DC voltage.

You can drive the coil of that relay with either AC or DC, but either way, if you lose voltage to drive the coil, the contact opens and isolates.

My point is, for simple grid-tied system, there is no need for a "stop" switch anywhere in the system. It doesn't matter whether the contactor coil is driven by the premise AC or by a DC power supply connected to the premise AC, when the the main is opened or the meter pulled, the array Dc will become isolate.

Therefore, there is no need for the "stop" switch and yet as I understand it, such a switch is now required by the Code. The switch is not needed but is required.

Mark Frye
_______________________________________________

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to