I have seen the  X240's  trip off like this when theyare over loaded. When this 
was happening to us the slave inverters had blown AC  boards and some times 
Control and FET boards too. We had a hard time diagnosing this as their  green 
lights were on.  Using a clamp on  amp meter on each inverter's AC IN conductor 
while charging with the gen set allowed us to compare their charging currents 
to each other. Typically the ones with blown  AC boards output would be close 
to zero amps. So the X240's were doing double duty and they will smoke too if 
the inverters aren't delta with. 


Sincerely, 
Chris Worcester
530-448-9692 
 Sent from my Galaxy S®III

<div>-------- Original message --------</div><div>From: Kevin Pegg 
<[email protected]> </div><div>Date:03/11/2015  1:19 PM  (GMT-08:00) 
</div><div>To: RE-wrenches <[email protected]> 
</div><div>Subject: [RE-wrenches] Outback quad stack X240 breaker tripping 
</div><div>
</div>Hello Wrenches, 

Customer in remote location has a strange situation come up on an existing 
system installed (by others) 6 or so years go. Quad stack VFX3648. 

Last night gen start was triggered by low voltage - a normal system operation. 

Approx 1h into charge, they lost 1/2 the circuits in house - L2 de-energized. 
Caretaker went to check power system and noticed the X240 breakers tripped. 
Tried to reset but it tripped out right away. So he left it as is and called me 
in the morning. 

Here's what I've been able to determine today: 

- The x240 is installed to bridge L1 & L2 on the load side. 
- with master inverter on, 3 slaves off, both L1 and L2 energized so suggests 
x240 is working. 
- within 10 seconds of generator on and charging, x240 breaker trips (and makes 
L2 go dark). 
- loads are minor, ~1,000 w of misc lights and such, isn't all loaded up on one 
leg. 

Appreciate any thoughts to remedy. I'm not as familiar with this config as 
others. 

Kevin Pegg
EA Energy Alternatives Ltd. 
37471 Hwy 16 E
Telkwa, BC  V0J 2X2
250-846-9888
Http://www.EnergyAlternatives.ca 



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to