Kevin,

Not sure what happened on the dropped communication, but I had responded to you 
last week with some possible answers and things to check.  I think I made the 
mistake of replying directly to your email address and not sending to the 
entire Re-Wrenches forum, sorry for that as I know this is information that 
could be helpful to others as well.

In any case, Tump is right -- on an existing system where everything has been 
working fine for some time but now isn't, the key is to isolate, isolate, 
isolate.  Turn off all AC input, output and transformer breakers, then wake up 
each inverter by increasing the Power Save Level Master Adjust one step at a 
time.  Confirm proper AC voltage line to neutral at the inverter's AC output 
terminals  - all breakers are still open.

Close the breaker to the X240 balancing transformer, then close the AC output 
breakers of one inverter at a time, starting with the Master.  Confirm that all 
inverters are on and have proper voltage and phasing by verifying proper AC 
voltage line to neutral, line to line as measured at the AC output terminals 
and to the output bus bars  - all inverters should show 120 L-N, and any 
inverters programmed as L1 Slaves should show 0v L-L to the Master and 240v L-L 
to L2 Slaves.  L2 slaves

This establishes a baseline to ensure that all the power electronics, 
magnetics, wiring and programming are working properly.

Next, start the generator and close all the input breakers.  Measure AC voltage 
at the inverter's input terminals, confirm that each is seeing the proper 
voltage and phasing.  Verify that the inverters sync to and connect to the 
generator, and begin to charge.  Measure the AC current on both phases of the 
generator, and verify that they are balanced.

Some potential issues are:

1.       Bad X240 breaker.  Take a spare, 20A 2 pole DIN.

2.       Transformer insulation damaged, typically by overheating.  Rather 
unlikely, but possible.

3.       Failed or mis-wired or mis-programmed inverter, likely on L2.  Due to 
the distance to the site, consider taking a replacement board set with you.  
Alternately, the system can operate on both legs with the other inverters, even 
if it's an uneven number, through OutBack Stacking until you can schedule 
another trip.

4.       Heavily imbalanced load or generator.

If the charging currents on the generator are imbalanced, one possible solution 
is to disconnect the neutral from the generator at the power system end.  This 
presents a pure 240v load to the genset, which will force the currents to be 
balanced on both phases.

Feel free to contact me directly if you have any problems or questions.

Best Regards,

Matt James
Applications Engineering Manager
OutBack Power Technologies Inc.
Direct:  (360) 618-4364
Cell:  (360) 618-2869

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Kevin Pegg
Sent: Monday, March 16, 2015 10:51 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Outback quad stack X240 breaker tripping

Thanks for everyone's advise on this one. I've done as much as I can working 
with the caretaker remotely and will need to attend myself with some test gear 
to fully diagnose. This site is remote (10h of driving then 1h boat ride). I 
generally make a point of avoiding Outback product so feel much better informed 
to diagnose when onsite - later in the week. Thanks.

Curious what is going on with Outback's tech support. I waited on hold for a 
bit on Wednesday, then left a message for callback and am still waiting for 
that callback 3 business days later.

My client is most upset that Outback can't even bother to return a tech call. 
His instructions to me are if we find multiple failed components in the system 
and not simple fixes to remove the gear and replace with "anything as long as 
it's not Outback".

Will advise the list what was discovered once onsite.

Kevin
-----Original Message-----
From: RE-wrenches [mailto:[email protected]]On Behalf 
Of frenergy
Sent: March 16, 2015 6:38 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Outback quad stack X240 breaker tripping
Kevin,

        Not to add any confusion but I recently had to re-program the slave in 
a 2 VFX with Xfrmr system as it was doing the same thing...the 2 pole xfrmr 
breaker was tripping when a moderate load was on.  Granted this was not 
happening during charging though.  I think I changed the slave from OB slave L1 
to OB slave L2 and all was good.  It doesn't seem likely the programming in 
your case would have been messed with having been working well for years prior. 
 Curious to hear though of a solution eventually.

Bill

Feather River Solar Electric
4291 Nelson St.
Taylorsville, CA  95983
530.284.7849 / 6544 fax
----- Original Message -----
From: Tump<mailto:[email protected]>
To: RE-wrenches<mailto:[email protected]>
Sent: Monday, March 16, 2015 5:39 AM
Subject: Re: [RE-wrenches] Outback quad stack X240 breaker tripping

Have you turned the breaker on the t240 to the off position? One does NOT have 
to have that operational for the system to operate correctly.The old t240 has 
about the same parasitic draw as an inverter. Isolate, Isolate, Isolate. If the 
system functions correctly w/ the t240 off and the stacking is correct on this 
q stack disconnect it(the t240). Otherwise I would remove the inverter com 
cables and only connect 1 pair of inverters at a time, reset the mate with the 
correct com cables connected to P1& P2. Sometimes something so simple as 
disconnecting & reconnection the mate can have quite a benefit. Again I would, 
if you are really stuck on having the t240 operational, then try it with each 
inverter as a single unit then try the second set of inverters. Disconnect the 
#s1&2 inverters and do the same; connect #s 3&4 P1 & P2, to see exactly which 
component may be your problem.
You are more then happy to contact me off list if you choose. contact info 
below. Tump
On Mar 15, 2015, at 5:04 PM, Jerry Shafer wrote:


 Wrenches
OK if the X240 blows the fuse which is on the output of the inverter while the 
inverter is charging, excessive current must be passing through from one 
inverter and back to the output of another inverter ( a form of AC coupling 
gone bad). The time delay fits as the inverter ramps up, I would look at the 
contactors in each slave as one may be hanging or ther may be a bad board, easy 
way to test is to isolate each inverter and with a amp meter connected at the 
X240 see if current goes away in the X240 as it should not be doing much with 
light loads on the "House" side of the inverters. The X240 is 25 amps while the 
inverters are 50 amps. Sounds like a interesting one to diagnose.
Jerry

On Wed, Mar 11, 2015 at 11:59 AM, Chris Worcester 
<[email protected]<mailto:[email protected]>> wrote:
Hi Kevin,
I have seen the  X240's  trip off like this when theyare over loaded. When this 
was happening to us the slave inverters had blown AC  boards and some times 
Control and FET boards too. We had a hard time diagnosing this as their  green 
lights were on.  Using a clamp on  amp meter on each inverter's AC IN conductor 
while charging with the gen set allowed us to compare their charging currents 
to each other. Typically the ones with blown  AC boards output would be close 
to zero amps. So the X240's were doing double duty and they will smoke too if 
the inverters aren't delta with.


Sincerely,
Chris Worcester
530-448-9692<tel:530-448-9692>
 Sent from my Galaxy S(r)III

-------- Original message --------
From: Kevin Pegg
Date:03/11/2015 1:19 PM (GMT-08:00)
To: RE-wrenches
Subject: [RE-wrenches] Outback quad stack X240 breaker tripping

Hello Wrenches,

Customer in remote location has a strange situation come up on an existing 
system installed (by others) 6 or so years go. Quad stack VFX3648.

Last night gen start was triggered by low voltage - a normal system operation.

Approx 1h into charge, they lost 1/2 the circuits in house - L2 de-energized. 
Caretaker went to check power system and noticed the X240 breakers tripped. 
Tried to reset but it tripped out right away. So he left it as is and called me 
in the morning.

Here's what I've been able to determine today:

- The x240 is installed to bridge L1 & L2 on the load side.
- with master inverter on, 3 slaves off, both L1 and L2 energized so suggests 
x240 is working.
- within 10 seconds of generator on and charging, x240 breaker trips (and makes 
L2 go dark).
- loads are minor, ~1,000 w of misc lights and such, isn't all loaded up on one 
leg.

Appreciate any thoughts to remedy. I'm not as familiar with this config as 
others.

Kevin Pegg
EA Energy Alternatives Ltd.
37471 Hwy 16 E
Telkwa, BC  V0J 2X2
250-846-9888<tel:250-846-9888>
Http://www.EnergyAlternatives.ca<http://www.EnergyAlternatives.ca/>



_______________________________________________
List sponsored by Redwood Alliance

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org/>

_______________________________________________
List sponsored by Redwood Alliance

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org/>


_______________________________________________
List sponsored by Redwood Alliance

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>

[email protected]<blocked::mailto:[email protected]%22%20%5Co%20%22blocked::mailto:[email protected]>
               
www.SWNL.net<blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
                Solarwinds Northernlights
       Serving Mid Coast Maine & Northern California
                         207-832-7574   Cl. 610-517-8401
                              Blair "TUMP" May

               ********  MAINE'S CHARTER ********
                      NABCEP    "Certified PV Installer"

              ********  MAINE'S CHARTER ********
                  Trace Xantrex "Certified" Dealer / Installer"



________________________________
_______________________________________________
List sponsored by Redwood Alliance

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to