You may want to contact the gen set manufacture to see if the genny can go
cold "freeze protection" at sub zero  because it may be required to operate
24/7in that condition. you may be able to install a thermostat to control
the block heater, this way its not always on.  PS I would use the Outback
products.
Jerry

On Thu, Apr 2, 2015 at 4:47 PM, Gary Higbee <[email protected]>
wrote:

> Wrenches,
>
> I'm curious what strategies you use to preheat a propane gen in cold
> climates. This is a large off-grid design in a sub-zero winter climate and
> ideal would be to turn on a block heater an hour or two in advance, then
> run the gen cycle. We plan to use either a Schneider XW or Outback Radian
> configuration (still very interested in which you'd use and why). We could
> set up a logic/relay system to first send the gen request to the heater for
> a while and then turn off and initiate a gen cycle but that would eliminate
> the ability for autostart on short notice. I've read of heat lamps on a
> thermostat, just wondering if you have seen other solutions.
>
> Thanks!
>
> Gary
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to