-------- Original Message --------
Subject: Re: [RE-wrenches] Gen preheat in cold climates
From:
[email protected]
Date: Fri, April 03, 2015 10:32 am
To: "RE-wrenches" <
[email protected]>
We are dealing with a generator that absolutely won't start
when cold, so
I was considering a block heater. Below 20 deg F it has
proven worthless,
and we can see -20 F on occasion.
My concern is using power from a low battery on a cold
cloudy day to heat
a generator. How long does it take to make a difference? Has
this method
proven 100% reliable?
Thanks,
Drake
> Hi Gary,
>
> We have implemented a preheat strategy that has really
worked well at a
> site using dual sunny islands. They have a load shed
function built in
> with the control relays. We are using that function to
add the block
> heater load. When a generator start is likely (~50%
SOC) it triggers a
> relay that energized the block heater. The generator
start is then
> programmed at a lower SOC (~30% SOC). It takes some
guesswork to know how
> many watt hours its going to take to get the block
heated up, but we
> conservatively chose and have fiddled with it. I
imagine this can be done
> with either the Radian or the XW, and you could trigger
with voltage
> instead of SOC, but SOC is a superior way to do it.
>
> Another way is to use a propane block heater. This will
work well, but
> they use quite a bit of propane, and are very expensive
(~$1500).
>
> Good luck
>
> On Thu, Apr 2, 2015 at 8:47 PM, Gary Higbee <
[email protected]>
> wrote:
>
>> Wrenches,
>>
>> I'm curious what strategies you use to preheat a
propane gen in cold
>> climates. This is a large off-grid design in a
sub-zero winter climate
>> and
>> ideal would be to turn on a block heater an hour or
two in advance, then
>> run the gen cycle. We plan to use either a
Schneider XW or Outback
>> Radian
>> configuration (still very interested in which you'd
use and why). We
>> could
>> set up a logic/relay system to first send the gen
request to the heater
>> for
>> a while and then turn off and initiate a gen cycle
but that would
>> eliminate
>> the ability for autostart on short notice. I've
read of heat lamps on a
>> thermostat, just wondering if you have seen other
solutions.
>>
>> Thanks!
>>
>> Gary
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address:
[email protected]
>>
>> Change listserver email address & settings:
>>
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>>
http://www.mail-archive.com/[email protected]/maillist.html
>>
>> List rules & etiquette:
>>
www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>>
www.members.re-wrenches.org
>>
>>
>
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address:
[email protected]
>
> Change listserver email address & settings:
>
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
>
http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
>
www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
>
www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance
List Address:
[email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org