That's a pretty good size battery bank compared to the charge coming in, 
normally you only see this with very small battery banks.

A battery when under charge is going thru a chemical reaction, this reaction 
doesn't immediately stop when you remove the charge, if you have a strong 
source on a small battery bank. The chemical reaction can keep going on for 
several minutes after the charge has been removed.  The battery isn't charging 
it's self the chemical reaction is just still continuing.

To test this, you can put a small DC load (couple of 12volt light bulbs in 
series) across the battery, when you shut off the controller, turn on the dc 
load for a second or two and see where the voltage is...

Compare it to cooking a roast... when you pull it out of the oven, it's still 
cooking for about 30-45 minutes past the time you remove it out of the oven.

Some controller manufactures will actually back feed the panels for a short 
period of time to regulate, and prevent the overvoltage.

On flooded batteries this isn't much of a problem, but VRLA's if the time is 
excessive it can be an issue in the long term for the batteries.

Just a note... those full rivers can accept a bit more voltage than a standard 
AGM...

http://www.fullriverbattery.com/product/batteries/DC400-6



From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Drake
Sent: Monday, May 18, 2015 4:58 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Xantrex C-40 Drifting

Hi Steve,

The battery bank consists of four, 415 AH in a Full River AGM deep cycle 
batteries wired  in a 24 volt series.

That is a new concept to me. Does the battery bank charge itself through its 
own chemical reaction? Would there be any issues with gassing in the VRLA 
batteries? Would you recommend doing anything about this situation, like change 
charge controllers?

Thanks,

Drake

Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328
http://athens-electric.com/


At 07:10 PM 5/18/2015, you wrote:

Content-Language: en-US
Content-Type: multipart/related;
         
boundary="_004_414D424906AE60489EF1829E1EFA55712C9C56F2sbcexchsbcdomai_";
         type="multipart/alternative"

Hey Drake,

How large is the battery bank?

I've seen this before on VRLA's with a couple of companies controllers. Usually 
this will happen with small battery banks.

Best way to explain it is when the battery bank is charging and you remove the 
charge, the battery is a chemical reaction... it's still charging for a short 
period of time even though you have removed the source.




Steve Higgins
Technical Services Manager
P: +1.902.597.4020
M: +1.206.790.5840
F: +1.902.597.8447
Surrette Battery Company
Exclusive manufacturer of
[[]]<http://www.rollsbattery.com>

From: RE-wrenches [ mailto:[email protected]] On Behalf 
Of Drake
Sent: Friday, May 15, 2015 7:10 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Xantrex C-40 Drifting

I was thinking of a Blue Sky or a Morning Star replacement.

The Full River AGM L-16 batteries recommend a 29.4 absorption, very high for a 
maintenance free battery. I've triple checked this one.

At 09:30 AM 5/15/2015, you wrote:

HI Drake,

Iv'e never seen this happen. Â
But have you considered a small morningstar or similar?

A question, you list 29.4v, that seems high?

jay



On Thu, May 14, 2015 at 5:12 PM, Drake < 
[email protected]<mailto:[email protected]>>
 wrote:
I have a Xantrex C-40 that won't keep its settings. It is important that it 
does because it is for a maintainer array (80 W) on an AGM battery bank, on an 
AC coupled backup system. Not only could high voltage damage the batteries, but 
when the voltage goes over 30 Volts, the AUX relay opens and the grid tie 
inverter is isolated from the grid.
After numerous sessions of reprogramming, Xantrex tech support sent me a new 
unit. The problem persisted as before. A new temperature sensor helped, but the 
settings still drift. It seems that rebooting the charge controller helps for a 
day or so, but then it drifts again.
The potentiometer settings are way below the calculated setting for 29.4 V, but 
it still peaks in the high 30s. I check the temperature compensated voltages on 
the Outback Mate, and the temp compensated voltage runs high.
In a related side issue, the AUX relay of the FX inverters is not based on 
temperature compensated voltage, which makes setting AC coupling charge set 
points more problematic.
Has anyone experienced a C-40 CC that drifts in its settings. What would be a 
good (inexpensive) charge controller to accurately control 80 W of PV?
Thanks,
Drake



--
Jay Peltz
Peltz Power
[email protected]<mailto:[email protected]>
_______________________________________________
List sponsored by Redwood Alliance

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org/>

This email and its attachments have been scanned by mailWatch E-Mail Firewall 
for viruses, spam, and malicious content. The information transmitted in this 
email is intended only for the entity or person to which it is addressed and 
may contain confidential/privileged material. If you received this in error, 
please contact the sender and delete the material from any computer. Any 
review, retransmission, dissemination, or other use of this information by 
persons or entities other than the intended recipient is strictly prohibited



_______________________________________________
List sponsored by Redwood Alliance

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org/>


This email and its attachments have been scanned by mailWatch E-Mail Firewall 
for viruses, spam, and malicious content.

The information transmitted in this email is intended only for the entity or 
person to which it is addressed and may contain confidential/privileged 
material. If you received this in error, please contact the sender and delete 
the material from any computer. Any review, retransmission, dissemination, or 
other use of this information by persons or entities other than the intended 
recipient is strictly prohibited
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to