Your assumption is the rule here. Metal inside a building envelope and it cannot transition at the penetration it must be metal before entry.
---------------------------------------------------------------------------- Dana Orzel Great Solar Works, Inc - NABCEP # 051112-136 E - [email protected] - Web - solarwork.com O - 970.626.5253 C - 208.721.7003 "Responsible Technologies for Responsible People since 1988" Please consider the environment before printing this email. -----Original Message----- From: RE-wrenches [mailto:[email protected]] On Behalf Of Christopher Warfel Sent: Monday, July 13, 2015 10:59 AM To: [email protected] Subject: [RE-wrenches] DC conductors in metallic raceway/conduit I was under the assumption that dc conductors could only be run inside a building when in metallic raceway/conduit (up to a readily accessible disconnect switch) . The building being occupied/residence. A contractor ran 5 feet of pvc from the wall penetration to the charge controller in a concrete block garage. I don't see anything that allows this by what I find in the NEC. Has anyone have a reference that permits this? Thank you for any assistance. -- Christopher Warfel, President ENTECH Engineering, Inc. PO Box 871, Block Island, RI 02807 401-466-8978 _______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org