My initial experience with Radians was not good. I had one of the 4kw modules 
fail three times on a 8048. Once was the result of a factory wiring error, 
plain as day when I went to replace it. Module 1 output was wired to module 2 
terminals on the AC board and vice-versa. But the communication cables were 
plugged in correctly (module 1 to jack 1, 2 to jack 2). This caused 
master/slave programming to get all screwed up. It worked for about 3 weeks 
before the right combination of commands occurred and it smoked.

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Rich Nicol
Sent: Friday, January 15, 2016 8:13 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] battery-based inverter

 

Had Radian failures and typical issues contacting Outback tech support in a 
reasonable amount of time. (ended up replacing boards on site, just like FX 
inverters, which is nice rather than sending the unit in)

Xantrex XW is massively improved after a rocky past, interconnect box is very 
spacious and easy to work in, and perhaps most important – tech support to 
assist with programming etc. has proved to be top notch and readily available 
when needed. All of this is counter to what our experience was historically 
with Xantrex but perhaps the Schneider purchase has made a positive impact?

RIch

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of [email protected]
Sent: Thursday, January 14, 2016 9:36 PM
To: RE-wrenches <[email protected]>
Subject: Re: [RE-wrenches] battery-based inverter

 

Kirk,  I agree with Peter.  I have installed several Radians with good luck.  I 
installed one SI and it worked ok but was more expensive and very time 
consuming to install.  Did one XW and would never do it again.  Never has 
worked right.

 

John

Central Vermont Solar & Wind

 

 



Sent from my iPhone


On Jan 14, 2016, at 7:37 PM, Peter Parrish <[email protected]> 
wrote:

My 2 centavos. Stick with them. I prefer their approach over SMA.

 

-          Peter

 

Peter T. Parrish, Ph.D.

President, SolarGnosis

1107 Fair Oaks Ave.

Suite 351

South Pasadena, CA 91030

(323) 839-6108

[email protected]

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Kirk Herander
Sent: Thursday, January 14, 2016 12:39 PM
To: RE-wrenches
Subject: [RE-wrenches] battery-based inverter

 

Hello,

Can anyone recommend a good battery-based inverter for grid-intertie? I need 
both generator and utility inputs, 120 or 240 output. I have experience with 
the OB Radian series but don’t know what else is out there. Thanks.

 

Kirk Herander

Owner|Principal, VT Solar, LLC 

Celebrating our 25th Anniversary 1991-2016

www.vermontsolarnow.com

dba Vermont Solar Engineering

NABCEPTM  2003 Inaugural Certificant

VT RE Incentive Program Partner

802.863.1202

 

 

 

 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to