Hi Todd

Yes the XW, Radian, FXR versions and the RE version from magnum
Have generator support. 

But that isn't what I was talking about in my last post. 

Jay

Peltz power. 

> On Jan 15, 2016, at 2:37 PM, [email protected] wrote:
> 
> the old sw inverters had something called "generator support", where if the 
> loads exceeded the generator's output, the inverter would forego charging and 
> sync with, and assist the generator's output.
>  
> the fx series does not offer this.
>  
> do the radian, xw or magnum inverters do this?
>  
> thanks,
>  
> todd
>  
>  
>  
>  
>  
> 
> 
> On Friday, January 15, 2016 2:08pm, "Kevin Pegg" 
> <[email protected]> said:
> 
> Hi Jay,
>  
> Thanks for your information. That generator mode sounds like an excellent 
> feature. I guess it is time to give the Radian an opportunity.
>  
> re: XW+ generator charging - interesting point as I was recently trying to 
> get an XW+ 6048 to play happily with an under-sized Honda EU6500 generator 
> and after hrs of tweaking was only able to make it successfully connect 
> without overloading the generator when input amps were set to 2/3 of 
> generators rated continual output. It would be nice to have a slower ramp up 
> to 100% charge rate - something they should be able to do via updated 
> firmware if anyone cared.
>  
> re: XW Power Distribution Panel. I will take credit for that! The first 
> prototype they showed us had these tiny wee little junction boxes reminiscent 
> of DR/SW days that was always lots of fun to cram in several # 6 conductors 
> (ideally when frozen). I lobbied hard for a huge box, and ultimately the end 
> product turned out quite well.
>  
> Kevin
>  
> From: RE-wrenches [mailto:[email protected]] On 
> Behalf Of jay
> Sent: January-15-16 12:15 PM
> To: RE-wrenches <[email protected]>
> Subject: Re: [RE-wrenches] battery-based inverter
>  
> HI Kevin,
>  
> I agree that tech support hasn’t been the been the best with OB, I do think 
> its getting better.
>  
> As to the charger issues.  The radian has a generator mode that as long as 
> its within voltage limits will use any frequency or harmonics and take it all 
> out.  Amazing.  I wrote here some months ago about a radian that ran the 
> house just fine, but with generator not.  And the generator by itself not 
> either.  But in the generator mode, it was perfect.  And its the only 
> inverter out there with this feature I know of.
>  
> And I’ve also just had to work on a set of new XW+ units. They seem to hit 
> the generator super hard on connection.  I had to set the total connection 
> watts to be quite low to make them work.  And that was after very long tech 
> support, that was no help at all. I think there just wasn’t anything they 
> could do.  The customer is having to install a much larger generator to make 
> his chargers work at higher settings.
>  
> A few other thoughts about these two inverters.
>  
> Radian is field repairable, XW not
> Radian has easy firmware upgrades, XW definitely not
> Radian has built in WWW access.  XW need addition hardware
> Radian has built in AGS, XW not
> Mate 3 easier to use than SCP.  Now I know this will be a huge argument,  but 
> try walking a customer through the AGS on a mate 3 vs SCP
> Generator mode on radian is amazing.  
>  
>  
> For the XW positives.  The XW BOS is large, easy to wire and will handle 3 
> inverters and 4 CC. I love that box.
> Vs the GS box which frankly is a joke.
>  
> So I choose the Radian.  its not perfect, but.
>  
> Jay
>  
> peltz power
>  
>  
> On Jan 15, 2016, at 11:59 AM, Kevin Pegg <[email protected]> wrote:
>  
> Interesting thread. Our firm wrote off Outback products several years ago for 
> two reasons:
>  
> 1) beyond abysmal tech support - when we have a problem we need to talk to a 
> skilled, knowledgeable tech, not some kid reading off a script designed for 
> end users; or to sit around for a call back that never happens. 
> 2) ongoing power quality problems when the inverter was in charge mode via 
> generator, some more sensitive loads would not operate, causing customers 
> complaints. Does this still continue with the radians? 
>  
> It is nice to hear that the radians install ok, though luck is not something 
> I like to count on working in the remote bush. I am more interested in Radian 
> installs that were challenging, and was Outback there to expeditiously 
> resolve the issues and have a happy customers?
>  
> My bias is towards the XW series. Our firm was involved in the design and 
> initial product testing of the XW system. It was a bit rocky at the start, 
> but has been a relatively stable product. The ability to remotely monitor and 
> program a customer's system is a big plus for a lot of our remote clients.
>  
> The two big complaints I have with the XW is the useless battery capacity 
> meter. I know there is an add on module available now but have not tested 
> that. Customers wonder why I put tape over the capacity indicator lights on a 
> brand new inverter. And the other is long term stability. We find in remote 
> automated unattended hybrid cycle charge sites that the inverter will at 
> least once a year screw up, resolved by a power cycle. So we just make it 
> part of maintenance routines to reboot the systems when we are onsite for 
> planned service.
>  
> We use SMA Sunny Island product for larger industrial projects. More 
> expensive, more difficult to set up, more difficult to program - but once 
> they are up and running solid with no issues and they take better care of 
> batteries through a smarter charging algorithm.
>  
> Kevin
>  
>  
> From: RE-wrenches [mailto:[email protected]] On 
> Behalf Of [email protected]
> Sent: January-14-16 6:36 PM
> To: RE-wrenches <[email protected]>
> Subject: Re: [RE-wrenches] battery-based inverter
>  
> Kirk,  I agree with Peter.  I have installed several Radians with good luck.  
> I installed one SI and it worked ok but was more expensive and very time 
> consuming to install.  Did one XW and would never do it again.  Never has 
> worked right.
>  
> John
> Central Vermont Solar & Wind
>  
>  
> 
> 
> Sent from my iPhone
> 
> On Jan 14, 2016, at 7:37 PM, Peter Parrish <[email protected]> 
> wrote:
> 
> My 2 centavos. Stick with them. I prefer their approach over SMA.
>  
> -        Peter
>  
> Peter T. Parrish, Ph.D.
> President, SolarGnosis
> 1107 Fair Oaks Ave.
> Suite 351
> South Pasadena, CA 91030
> (323) 839-6108
> [email protected]
>  
> From: RE-wrenches [mailto:[email protected]] On 
> Behalf Of Kirk Herander
> Sent: Thursday, January 14, 2016 12:39 PM
> To: RE-wrenches
> Subject: [RE-wrenches] battery-based inverter
>  
> Hello,
> Can anyone recommend a good battery-based inverter for grid-intertie? I need 
> both generator and utility inputs, 120 or 240 output. I have experience with 
> the OB Radian series but don’t know what else is out there. Thanks.
>  
> Kirk Herander
> Owner|Principal, VT Solar, LLC
> Celebrating our 25th Anniversary 1991-2016
> www.vermontsolarnow.com
> dba Vermont Solar Engineering
> NABCEPTM  2003 Inaugural Certificant
> VT RE Incentive Program Partner
> 802.863.1202
>  
>  
>  
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
>  
> 
> 
> 
> Sent from Finest Planet WebMail.
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to