The testing that we have done with our batteries, is well over 90% completed 
has actually increased cycle life and performance even at the higher charging 
voltages… We are testing at 2.6vpc just for your information, these batteries 
have actually tested at over 110% capacity.  That being said this is also in a 
lab, where temps are controlled.. In a “real world” situation temperatures are 
a killer for any manufactures batteries, this is why all systems need a BTS 
installed.   It’s hard to believe how many don’t install them, nor do they 
install them  correctly…  As all of you know they should be on the side of the 
battery, below the level of the plates, this is normally about 1/3 to ½ way 
down the battery.   They should never be on the top.



From: RE-wrenches [mailto:[email protected]] On Behalf 
Of RE Ellison
Sent: Tuesday, January 19, 2016 7:07 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Battery Charge Settings.

OK Steve now you got me thinking,
Some would say that's a bad idea!

Using the voltage settings you're speaking of what would you recommend for 
equalize charging ?

I have always thought that different settings for different times of year was 
logical but you're getting your bulk up you know what I would normally consider 
to be a low side of the equalization charge.

Understood that rolls charge differently than a lot of other batteries I 
believe it's due to plate density?

Thanks,
bob ellison

On Jan 19, 2016, at 8:52 AM, Steve Higgins 
<[email protected]<mailto:[email protected]>> wrote:
Good Morning Wrenches…

I’d like to take the recent Trojan thread to throw this out there!

With the IEC certification, many battery manufactures are being forced to 
recommend higher settings to charge their batteries.   The problem with off 
grid systems, or even some grid back up systems is the settings can/will vary 
from end user to end user and can be very difficult to determine.   Try to 
avoid setting up a system and assuming that those settings will be good year 
round as settings in most systems need to adjusted at least twice, sometimes up 
to three times a year.

For example, we are almost finished with IEC testing, the way they do this 
testing in short is they take a battery, charge it to full using mfg suggested 
settings, discharge it to 100% and they cycle the battery until it comes to 
full capacity.    Don’t quote me, but IEC testing requires the batteries to 
come to full charge within the first 8-10 cycles.   To do so, you need to be 
very aggressive on the charging settings.

Now, most customers don’t cycle to 100% depth of discharge so end users don’t 
need to be so aggressive on charger settings, but we will be publishing revised 
charging parameters and instructions in the coming quarter.   Bottom line, 
Bulk/Absorb Voltages @ 25 Deg C you will be advised to charge the Rolls 
Batteries at 2.45 to 2.5vpc.  This number will vary based on how much the 
customer is using the system.  A weekender cabin with a decent sized  array 
(<10% of C20 Charge Current) will need closer to 2.4 to 2.45vpc, while a full 
timer (daily heavy cycles)  will need a setting closer to the 2.5vpc rating.

Remember, regardless of where you are in the world, unless the batteries are 
installed in a temperature controlled room where it fluctuates less than ½  
degree C, you should ALWAYS, ALWAYS use battery temperature compensation.   
Failure to do so, will always result in premature failure of the batteries.

Settings are generally a suggestion, the problem is they (customers) should be 
looking at the SG’s at least on a quarterly basis and adjusting settings when 
necessary.   Lower trending SG equal higher settings, higher SG equal lower 
settings.  I find that too many people set up settings and forget them, until 
they have a problem.   Normally I find with most customers they should have a 
bit lower settings from April to Sept, while settings should be higher from Oct 
thru March.

Remember, the battery companies you are dealing with generally don’t have a lot 
of experience in solar… they are used to industrial applications where you see 
8-12 hours of charging every single day.    We all know that in most Off grid 
systems you are lucky to get 3-5 hours, at best of decent charging a day.




Steve Higgins
Technical Services Manager
P: +1.902.597.4020
M: +1.206.790.5840
F: +1.902.597.8447
Surrette Battery Company
Exclusive manufacturer of
<rollsae305d>

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Theo Van
Sent: Monday, January 18, 2016 8:44 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Trojan L-16 charge settings


No "settings recommend by Trojn"were shown.
On Jan 18, 2016, at 6:43 PM, William Miller 
<[email protected]<mailto:[email protected]>> wrote:
Colleagues:

I have an off-grid customer for whom I replaced a set of 8 Trojan L-16s as well 
as upgrading her inverter and charge controller.  Right after the job, we found 
several batteries with low specific gravity.  We spoke with the local 
distributor and received two replacement batteries.

The system continues to perform poorly.  The customer EQs every 30 days to 60 
plus volts for 3 hours.  They try to get a full bulk and absorption charge in 
every day but this time of year may not. The specific gravity readings continue 
to diverge and generally go lower.

We contacted the distributor who told us they have had problems with Trojan 
batteries since the company was sold about two years ago.  We were told they 
had a brand X battery that tested better than the Trojans.  We agreed to try 
the Brand X but then were told that we had not charged the Trojans adequately.  
Below are the settings recommended directly by Trojan

These settings are significantly higher than any I have used before.  Also, I 
don’t recall it being possible to set different bulk and absorption voltages 
with any of the equipment I use.  I use Trace, Outback, Schneider default 
settings of 57.6 bulk, 54.4 float and reprogram to 60.5 for equalization.

I am curious about what charge settings you find successful for flooded 
lead-acid batteries and what any of you might think about the recommended 
settings as seen below. Do you feel it is practical to achieve these settings 
in an off-grid scenario?  Would these high settings cause excessive water 
consumption?

Thanks in advance.

William Miller

<image001.jpg>
Lic 773985
millersolar.com<http://www.millersolar.com/>
805-438-5600



I looked at the spreadsheet and the SG. readings across each battery are 
uniform which tells be that it is highly unlikely that anything is wrong with 
the batteries except for being under-charged. Take a look at our User’s Guide 
on the Trojan website on page 19  ( Recommended Charge Profile) or FLA 
batteries.
The Bulk stage should be @ 59.3V, Absorb @ 58.8V, Float @ 54V and Equalization 
@ 64.8V. When the User notices drops in the SG such as in this document, an EQ 
charge should be performed in order to get the batteries back up to full charge 
(full charge SG being in the range of 1.270 to 1.280. When performing the EQ, 
the user should take SG reading for a “pilot” battery every 30 minutes until 
the voltages reach that range. Termination should happen when SG reaches full 
charge range or if battery temperature reaches 112 degrees F, which-ever comes 
first. SG readings can be taken during EQ, but you have to make sure that you 
bump the tiny gas bubbles off the Hydrometer float to prevent erroneous 
readings.
Seeing the SG readings decreasing after each month is an indication that maybe 
the Absorb Time needs to be increased, maybe from 3 hours up to 4 or 5 hours.

_______________________________________________
List sponsored by Redwood Alliance

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>

This email and its attachments have been scanned by mailWatch E-Mail Firewall 
for viruses, spam, and malicious content. The information transmitted in this 
email is intended only for the entity or person to which it is addressed and 
may contain confidential/privileged material. If you received this in error, 
please contact the sender and delete the material from any computer. Any 
review, retransmission, dissemination, or other use of this information by 
persons or entities other than the intended recipient is strictly prohibited
_______________________________________________
List sponsored by Redwood Alliance

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>

This email and its attachments have been scanned by mailWatch E-Mail Firewall 
for viruses, spam, and malicious content.

The information transmitted in this email is intended only for the entity or 
person to which it is addressed and may contain confidential/privileged 
material. If you received this in error, please contact the sender and delete 
the material from any computer. Any review, retransmission, dissemination, or 
other use of this information by persons or entities other than the intended 
recipient is strictly prohibited

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to