I have long been a fan of aggressive charge voltages for flooded batteries in 
daily cyclical use. As Steve has emphasized, temp. comp. is imperative, 
especially using higher absorb voltage as over-voltage at high cell temperature 
rapidly reduces cycle life. 

It is my observation that most L16 size batteries don’t do well with lower 
absorb voltages and I have seen more Trojan L-16 failures than I care to. For 
L16’s, I recommend 2.5Vpc with extended absorb time until current drops to  
0.5A/100AH C. 

Steve, I concur with your finding about higher voltages. Here’s something I 
have been doing with success: I have been testing CC/CV/CC charge regime, also 
called IUI. This provides what I call a mini EQ cycle prior to entering Float 
charge. Every day when the absorb timer terminates, I start the EQ cycle for 
about 30 minutes. This drives the voltage up to 2.65Vpc. The current is 
naturally limited by battery resistance since the battery is nearly full. The 
results have been impressive for battery life and capacity recovery. Here’s 
some examples...

1. A customer using this method with Lifeline AGM batteries is in the 10th year 
of use with only about 20% capacity degradation. 
2. Another customer that has 5 year old T-105 batteries began doing this about 
6 months ago and has reported capacity being increased.
3. Another has Rolls 530’s (we did not sell or install) in a 12 volt system. 
After 2.5 years he came to us with the capacity problems. His chargers were set 
to 2.4Vpc and he had not performed any EQ cycles as mandated. We installed a 
charger capable of EQ voltages and began the daily EQ cycle and he too has 
reported capacity recovered.

I think it is worthwhile to consider higher charge voltage and/or trying the 
IUI charge method for anyone experiencing battery capacity loss. 

Larry Crutcher
Starlight Solar Power Systems




On Jan 19, 2016, at 9:01 AM, Steve Higgins <[email protected]> wrote:

The testing that we have done with our batteries, is well over 90% completed 
has actually increased cycle life and performance even at the higher charging 
voltages… We are testing at 2.6vpc just for your information, these batteries 
have actually tested at over 110% capacity.  That being said this is also in a 
lab, where temps are controlled.. In a “real world” situation temperatures are 
a killer for any manufactures batteries, this is why all systems need a BTS 
installed.   It’s hard to believe how many don’t install them, nor do they 
install them  correctly…  As all of you know they should be on the side of the 
battery, below the level of the plates, this is normally about 1/3 to ½ way 
down the battery.   They should never be on the top.
 
 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to