We were discussing remotely turning on and off the inverter itself like with the Outback's remote on/ off terminals. Magnum only has their remotes which aren't compatible with other systems.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 3/15/2016 8:04 PM, [email protected] wrote:


On 3/15/2016 5:23 PM, Ray Walters wrote:
Hi Brad;

I think that remotely tripping the inverter might work with Outback, but definitely not with Magnum. (I checked with them today) Also, if the battery cables are more than 5 ft long, the rapid disconnect /might/ have to be closer to the batteries. (/690.12 ...shall apply only to PV system conductors more than 5 ft in length inside the building...)
/
*

Ray,

There is no reason at all that any battery based inverter should not work with our RSS system.

Did they give you a reason why the inverter can't be turned off by switching off its battery circuit breaker ?

I almost always turn off a Magnum inverter (or other inverter) by switching off its battery breaker, at least when we're testing an E-panel system. Works every time except maybe if the grid is or generator is connected and running. In a shutdown condition, those two things would
be dead and inactive.

Also, Our 600V Cat5 cable is USE-2 rated, shielded and tougher than nails.

Thanks and hallucinations,
boB
*

/
/As for inverter and overall system reliability? I'm afraid that//is going 'Rapidly' down hill.// Decades//of experience says that the more gizmos and automatic controls you add, the more chances you have for something to go wrong. The Birdhouse system defaults to/'off' /with any communications problems, so one CAT 5 cable has a nick in it, and the entire system crashes.//With all this emphasis on safety, we also need to be thinking about our customers living alone in cold, remote locations./
/Perhaps an emergency disconnect for the emergency disconnect?
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 3/15/2016 5:45 PM, Bradley Bassett wrote:
I've been promoting the use of the remote on/off terminals that are available in most inverters, which can be connected to the AUX in the Birdhouse. For a very minimum effort and cost, the inverter AC output would be shutdown when the rapid shutdown is activated. I think using the remote on/off terminals seems a lot cleaner way to do this than disconnecting the battery cables. And there is the possibility that disconnecting the battery from a fully loaded inverter may damage the inverter, do we really want to risk that whenever we test the RSD system? None of the current inverter mfg will say that this will do any damage, but they don't seem very convinced to me. I remember a decade ago when they did say there could be an issue. I'm not sure how much different inverters are now than then.

Brad
AEE Solar

On Tue, Mar 15, 2016 at 12:48 PM, Patrick Shortell <[email protected]> wrote:

    Dear List,
    Maybe it's an over simplistic opinion, but shouldnt all sources
    be disconnected rapidly in an emergency situation.
    We can always do better than what the code requires. I get
    frustrated when people go to the book, (and try to hide behind
    the text).  instead of thinking through real life scenarios.
    There are simple ways to work around these issues.
    I find when something is questionable, Ill call the AHJ and get
    his approval First.
    What would I do in my own house?
    What if someone thought all the power was off when they dragged
    a hoseline into my basement.
    My two cents
    Pat

    On Tue, Mar 15, 2016 at 1:10 PM, <[email protected]> wrote:

        Ray,

        I guess I have to step in after that acknowledgement. PV
        system circuit is a
        self-defined term and therefore cannot be defined unless you
        are going to
        develop a meaning that is different from the
        self-definition. It means ANY
        circuit in a PV system. This includes battery and
        stand-alone circuits in
        the 2014 NEC.

        The language of the 2014 NEC was a compromise between the
        fire service and
        the PV industry.  Originally, the language required
        essentially module-level
        shutdown. I raised the concern with the PV industry to get
        them involved
        since most were not paying attention at the time. This
        language was
        developed and intended to cover all circuits in a PV system.
        In the 2014
        NEC, batteries are part of a PV system and therefore fall
        under this
        requirement.

        In the 2017 NEC, we were very careful to carve out all
        batteries and loads,
        that were previously part of PV systems, and place them in
        their own
        articles. Don't shoot the messenger on this one and don't
        think for a minute
        that I alone made this requirement or am alone in
        interpreting it in this
        way. I did author this compromise with other representatives
        of the PV
        industry so I think I know what the intent was.

        It is understandably difficult for battery systems and I
        would try to keep
        battery circuits as short as possible. The 5-feet was
        intended to match the
        requirement of 690.71(H)--which is further evidence of the
        intent of the
        2014 NEC.

        The 2017 NEC removes batteries from the requirement, but
        they still cannot
        backfeed the PV array. Energy storage systems (Article 706)
        will have their
        own requirements in time--that is guaranteed.

        Bill.


        -----Original Message-----
        From: RE-wrenches
        [mailto:[email protected]] On
        Behalf Of Ray Walters
        Sent: Tuesday, March 15, 2016 9:02 AM
        To: RE-wrenches <[email protected]>
        Subject: [RE-wrenches] Rapid Shutdown

        Greetings Esteemed Wrenches:

        I've just heard back from our inspector here in Colorado,
        and we are still
        being required to disconnect the batteries under 690.12.  No
        where in 690.12
        are batteries mentioned, nor in the appropriate 690.71
        section that deals
        with batteries.  The entire reasoning behind this is based
        on a single
        article written by a single person: Bill Brooks.  I have
        contacted both
        Outback and Magnum on this issue, and their engineers are
        unaware that rapid
        shutdown applies.
        My interpretation is that I could install an inverter and
        battery system
        that was charged from a generator, and we would not need any
        rapid shutdown
        at all.  But according to Bill, as soon as I put a single
        solar module into
        the system, suddenly the entire system becomes PV? The
        problem lies with the
        term 'PV System circuit'  used in 690.12. 690.2 Defines 'PV
        Output
        circuit', and 'PV source circuit', but there is no 'PV
        system circuit'
        defined.  690.12 therefore uses an undefined term.
        Our design uses 2 inverters, so if we used Midnite's E panel
        with their
        remote trip breakers, the 2nd inverter would be more than 5
        ft from the
        batteries.  If we used Magnum or Outback DC disconnects
        (that would comply
        with the 5 ft rule specified in 690.71) they don't offer
        remote trip.
        We have a Midnite Rapid disconnect Combiner on the roof with
        the Birdhouse,
        so we are complying with 690.12, it should not be applied to
        batteries
        though.

        Thanks,

        --
        R.Ray Walters
        CTO, Solarray, Inc
        Nabcep Certified PV Installer,
        Licensed Master Electrician
        Solar Design Engineer
        303 505-8760 <tel:303%20505-8760>

        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: [email protected]
        <mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive:
        
http://www.mail-archive.com/[email protected]/maillist.html

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org <http://www.members.re-wrenches.org>

        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: [email protected]
        <mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive:
        
http://www.mail-archive.com/[email protected]/maillist.html

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org <http://www.members.re-wrenches.org>




-- Patrick A. Shortell
    /Licensed Master Electrician/
    /Certified Solar Installer/
    71 Oregon Street
    Long Beach N.Y. 11561
    cell: 516-477-0221 <tel:516-477-0221>





    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: [email protected]
    <mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/[email protected]/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>





_______________________________________________
List sponsored by Redwood Alliance

List Address:[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org




_______________________________________________
List sponsored by Redwood Alliance

List Address:[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org




_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to