In some jurisdictions and for some utilities, pulling the meter is a MAJOR
ordeal. Some jurisdictions require a "service change" permit on top of the
solar permit just to have the meter pulled. It also requires getting an
inspector out there at the perfect time to have it inspected so the the
utility will re-install the meter. The homeowner is often without power for
several hours, which is usually somewhere between inconvenient and
unacceptable. Insulation piercing taps are extremely common around here for
these reasons. With proper safety precautions and experience, I don't see
any issue specifying and using them.


Jason Szumlanski




On Wed, May 11, 2016 at 12:26 AM, Shasta Daiku <[email protected]>
wrote:

> Kirpal, I’m curious what the reason is for making the tap on an energized
> line. Why not have the meter pulled? While insulation piercing taps are
> designed for “hot work”, there use for that should be limited to tapping
> conductors that have OCP, and aren’t under load, with generous working
> space, like in a piece of switch gear. Even in that situation, making taps
> on energized conductors should only be done when it’s an absolute
> necessity. I’ve got a large body of “hot work” under my belt, both line and
> load side and will say that face shields and hot gloves saved my butt on
> several occasions and I’ve got a nice scar on my neck from a molten piece
> of lug from a main breaker that broke apart while I was tightening up it’s
> mounting screw. Stuff happens. It’s always best to play it safe.
>
> Michael Morningstar
>
>
> On May 10, 2016, at 11:04 AM, Chris Mason <[email protected]>
> wrote:
>
> This is what we use - we keep a selection in the van for difficult jobs.
>
> Insulation Piercing Connector 2/0-10 AWG
> Part #IPCS2001
> Insulation Piercing Connector 2/0-10 AWG 2/0-4 Main, 10-14 AWG Tap, Dual
> Rated AL9CU, Torque Limiting Nut
>
> On Tue, May 10, 2016 at 1:27 PM, Kirpal Khalsa <[email protected]>
> wrote:
>
>> Hi Folks,
>> We have a job requiring a supply side connection.  Wondering if anyone
>> could share some makes and models for connectors connecting to the wires
>> between a main meter and the main breakers in the electrical panel.
>> Ideally it would be able to be done hot.
>> I am also looking into the ConnectDer meter collar but will have to
>> coordinate with the utility for that and am looking to keep things simple.
>> Thank you!!!!
>>
>>
>> Sunny Regards,
>> Kirpal Khalsa
>> Oregon LRT#25
>> NABCEP Certified PV Installation Professional
>> Oregon Solarworks LLC
>> www.oregonsolarworks.com
>> 541-299-0402
>>
>>
>
>
> --
> Chris Mason
> NABCEP Certified Solar PV Installer™
> Solar Design Engineer
> Generac Generators Industrial technician
>
> www.cometsolar.com <http://www.cometenergysystems.com/>
> 264.235.5670
> 869.662.5670
> Skype: netconcepts
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to