Yes, by manually disconnecting the power but as mentioned not with the auto 
reboot with Rev. 15.  

 

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of William Miller
Sent: Monday, May 16, 2016 3:06 PM
To: 'RE-wrenches' <[email protected]>
Subject: Re: [RE-wrenches] Optics RE reliability

 

Gary:

 

Are you able to reliably re-establish connectivity by rebooting the Mate3?  

 

I was informed today that the power to the Mate3 is on the Orange/White pair.  
I have the ability to control a relay remotely that could open a relay on these 
leads.  If this will reestablish communications, then this might be a solution. 
 (The device has a ping function wherein you can program it to ping an IP 
address and perform a prescribed action if the ping fails after a programmable 
number of attempts over a programmable time period.)

 

Thanks,

 

William

 

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Gary Rochlin
Sent: Monday, May 16, 2016 2:37 PM
To: 'RE-wrenches' <[email protected] 
<mailto:[email protected]> >
Subject: Re: [RE-wrenches] Optics RE reliability

 

We have been having problems with the Mate 3 Optics RE since we installed it at 
the beginning of 2014.  Ours is a battery backup system for a grid tied 
install.  We just got off the phone with Outback this morning after upgrading 
to Rev. 15 two months ago and we are still having the going offline issue.  
Currently we have only been able to keep the monitoring running for about half 
a month and then it needs to be manually rebooted even with the 4-hour reboot 
function activated.  This morning we went out to the site to replace the 
original Mate 3 and tech support told us we would lose all historic data on the 
site - We had to pull off again.  The only saving grace is the solar system is 
still working as planned providing power to the back-up system we just can’t 
see the metrics and this is the last thing we expected from Outback when we 
made the choice to utilize the Radian system instead of the SMA sunny Island.  
From what I can tell Outback released their new system without sufficiently 
beta testing the monitoring and we are all paying for it.  

 

Gary Rochlin

 

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Chris Mason
Sent: Monday, May 16, 2016 1:15 PM
To: RE-wrenches <[email protected] 
<mailto:[email protected]> >
Subject: Re: [RE-wrenches] Optics RE reliability

 

We have reported to Outback that the Mate3 OpticsRE will stop reporting if the 
internet goes down for a while. In the Caribbean, we have some outages and the 
M3 does not handle them well. I think there is an option to reboot the M3 
daily,  I would try that. You can be pretty sure it is not a cable failure. 

On May 16, 2016 4:07 PM, "William Miller" <[email protected] 
<mailto:[email protected]> > wrote:

Friends:

 

We just installed our first Optics RE systems.  They are both at the same 
location connected to a satellite data system.  In the three weeks these two 
systems have been on line, they have become disconnected several times.  The 
latest time both Mates disconnected but we were able to reconnect one by 
remotely rebooting the router.

 

I have invested a lot of money, time and reputation on these systems.  I am 
hoping reliability improves.  I am on a long hold with Outback right now in an 
attempt to trouble shoot. I am guessing the resolution will be a two hour drive 
each way to unplug and plug the Cat5 cable in.

 

Ten minutes later:  I received helpful information from Outback tech support, 
as usual. I will be swapping Mates to see if the trouble moves, etc.  I will 
also be setting the auto reboot function.  

 

Can anyone else suggest how to resolve these issues?

 

What experience have the remainder of you had with the Optics RE system?  Is it 
reliable for you?

 

Thanks in advance,

 

William Miller

 

 

 

 

 


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected] 
<mailto:[email protected]> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org